Answer / pswin
You ask the value between L,N and E. So I will assume that you will test for single phase and the test voltage must be 500 v scale and full scale is 100 mega ohm.Minimum value should be 0.5 mega ohm between each conductors. If lower than that value, the cable or wire is not certified to use. For three phase, above answer is acceptable,too.
| Is This Answer Correct ? | 16 Yes | 3 No |
WHATS THE DIFFERENCE IN USING THE 125% AND THE 250% FACTOR OF SAFETY IN CALCULATING CIRCUIT BREAKERS CAPACITY IN MOTOR APPLICATION??
How star and delta connections inherently eliminate triplend harmonics?
what is meant by distance protection ? how distance protection relay function ?
What is open loop and control loop systems?
why battery set is required for D.G.set?
why we use perllel conection system in the wiring?
please explain me about traction application?
How to conduct the Magnetic Balance test on Power Transformer?
how to choose the cable rating for load (KW)? EXAMPLE.50KW load
14 Answers ACC, NCUI, Polycab, PowerSol, Siemens, SW,
why do we use spark detector inside the slip ring brush compartment 0ona slip ring induction motor?
how many types of cbs?with pcific ratings?
Induction motor & transformer both has magnetic core,then why induction motor is a inductive load & transformer not???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)