Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

what are the standard values for resistances(Megger testing)
between L&N, L&E and N&E (L=Live,N=Neutral, E=Earth)?

Answer Posted / pswin

You ask the value between L,N and E. So I will assume that you will test for single phase and the test voltage must be 500 v scale and full scale is 100 mega ohm.Minimum value should be 0.5 mega ohm between each conductors. If lower than that value, the cable or wire is not certified to use. For three phase, above answer is acceptable,too.

Is This Answer Correct ?    16 Yes 3 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is difference between insulating medium and fault current interruption medium in a switching device.

1632


What is sensitivity of a measurement?

1116


what is the current density of copper & alluminium.

2037


is it possible to say motor horsepower number without seeing name plate(when name plate damaged)

2063


how harmonics generated in induction furnance? how minimise it?

1989


Can we put 3 layers of cable tray while installing tray

2381


An ELHNC 80amp 240v 30mA RCD is tripping periodically, every 30 - 180 seconds is it safe to disconnect the protection circuit?

2132


what is the function of bearing in dc mchine" and where it is placed

2571


What is formula calculation size cable wire ?

1930


What is the meaning of dedicated earthing?

2141


What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?

2629


explain single phase series motor

1930


Define the three phase formula fuse.

1844


What fomula is used to calculate: 1. rated frequency withstand voltage, and 2. rated lightning impulse withstand voltage.

1694


what is the purpose of shading ring or shading coil in electrical equipments.

4457