For a certain load i need 100kw load ,In that case what
rating mccb should i use?
Answers were Sorted based on User's Feedback
Answer / chintan patel
It can be different for DC , 1phase AC , 3 phase AC , systems,
Lets calculate for all ,
1 ) For DC ( you have not mentioned Voltage but considering 230 V )
100 kw means 100000 watt
formula for DC power p= vi
100000= 230xi
i=100000/230= 434 amp
we always use current rating of the mccb is 1.5 times of full load current so we can use 434x1.5= 652 amp.
( if system is not running on full load select 630 Amp MCCB, if its on full load select 800A )
2 ) For 1phase AC,
Power: P = V I cos phi ( cos phi is power factor is not known assume 0.8 )
100000 W = 230 x I x 0.8
I = 543 Amp
we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 543 Amp X 1.5 = 815 Amp
select 800 Amp MCCB
3)
If load is 3 phase AC ,
Power P = sqrt(3) x V x I x cos phi
100000 w = 1.73 x 415 x I x 0.8
I = 174
we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 174 Amp X 1.5 = 261 Amp
( if system is not running on full load select 250 Amp MCCB,
if its on full load select 315 A )
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kalyan sharma
for 100 kw we will use 3 phase supply inplace of single
phase.
use formula p= 1.732 vi cosphi
100= 1.732*0.415*0.8*I
I = 174 amp
we always use current rating of the mccb is 1.5 times of
full load current so we can use 250 AMPs MCCB.3P/4P.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / rajat
for 100 kw means 100000watt
use formula p= vi
100000= 230xi
i=100000/230= 430 amp
we always use current rating of the mccb is 1.5 times of full load current so we can use 430x1.5= 645 amp
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / r g walia
for 100kw load required 630 amp mccb will be used.
| Is This Answer Correct ? | 2 Yes | 3 No |
what is the purpose of interpose t/f in control and relay ckts?
If I want to lift the water at a height 50m from ground level through two inch(diameter) metal pipe then what is the capacity of motor pump is required? is it possible in single phase supply or not?
How to check the cable fault / hv test of transformer cable.
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
Without seeing the nameplate descriptions of a rotating machine,Is it possible to say which one is a motor and which one is a generator? How would you certain this?
I have experienced electrical maintenance HT ,but I completed be ECE ....can I apply c license or not ???? Pls help me friend s...
What will happen if a dc source is given to a tubelight. Will it work or wont it work....
what do you mean by the "bay" in a switchyard? how to determine exact number of bays in a substation?
why capacitor is not discharged phase to body
Explain why the Voltage drop will happen in 3 Phase line?
what will happen if we give a dc supply to a transformer.?
What is the minimum load that you can keep in a 3 Phase 40 KVA Diesel Generator? Is it neccessary to load all the 3 phases? Can a phase be left without load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)