Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


For a certain load i need 100kw load ,In that case what
rating mccb should i use?

Answers were Sorted based on User's Feedback



For a certain load i need 100kw load ,In that case what rating mccb should i use?..

Answer / chintan patel

It can be different for DC , 1phase AC , 3 phase AC , systems,

Lets calculate for all ,

1 ) For DC ( you have not mentioned Voltage but considering 230 V )

100 kw means 100000 watt

formula for DC power p= vi

100000= 230xi

i=100000/230= 434 amp

we always use current rating of the mccb is 1.5 times of full load current so we can use 434x1.5= 652 amp.
( if system is not running on full load select 630 Amp MCCB, if its on full load select 800A )


2 ) For 1phase AC,

Power: P = V I cos phi ( cos phi is power factor is not known assume 0.8 )

100000 W = 230 x I x 0.8
I = 543 Amp

we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 543 Amp X 1.5 = 815 Amp
select 800 Amp MCCB

3)

If load is 3 phase AC ,

Power P = sqrt(3) x V x I x cos phi

100000 w = 1.73 x 415 x I x 0.8
I = 174

we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 174 Amp X 1.5 = 261 Amp

( if system is not running on full load select 250 Amp MCCB,
if its on full load select 315 A )

Is This Answer Correct ?    3 Yes 0 No

For a certain load i need 100kw load ,In that case what rating mccb should i use?..

Answer / kalyan sharma

for 100 kw we will use 3 phase supply inplace of single
phase.

use formula p= 1.732 vi cosphi

100= 1.732*0.415*0.8*I

I = 174 amp

we always use current rating of the mccb is 1.5 times of
full load current so we can use 250 AMPs MCCB.3P/4P.

Is This Answer Correct ?    3 Yes 1 No

For a certain load i need 100kw load ,In that case what rating mccb should i use?..

Answer / rajat

for 100 kw means 100000watt

use formula p= vi

100000= 230xi

i=100000/230= 430 amp

we always use current rating of the mccb is 1.5 times of full load current so we can use 430x1.5= 645 amp

Is This Answer Correct ?    5 Yes 4 No

For a certain load i need 100kw load ,In that case what rating mccb should i use?..

Answer / r g walia

for 100kw load required 630 amp mccb will be used.

Is This Answer Correct ?    2 Yes 3 No

For a certain load i need 100kw load ,In that case what rating mccb should i use?..

Answer / siddhart jha

mccb of 250 A/440V MUST BE USED FOR THAT.

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

Difference between on line capacitor and Station type capacitor.

1 Answers  


application s to shunt coil

0 Answers  


what is the meaning of 16/20 mva of transformer

7 Answers   JSW,


what is mean by PIR in circuitbreaker and give me detail of that?

0 Answers  


I have 30KW Motor Starter Panel, System voltage is 480V, So i have to convert voltage 480 to 220V to give the contactor coil. How i can select control transformer, Which rating transformer i can use this panel, what is the procedure, please tell me.

2 Answers  


what is calculation mathod/formaulla for deciding Size of busbar (Copper/ aluminum)for L.T. panel on Various Fault level like 50kA,25kA,10kA

0 Answers   Mega Power,


we all know that in capacitor there will be no ay physical connection between the two electrodes of the capacitor ,and the charge is stored between these electrodes during charging , so with out any physical connection how these charge is transferred from one plate to the another plate during the discharge?????

1 Answers  


draw waveform of capacitor or inductor in a d.c ckt(during transient) with zero resistance with it(in series or parallel)also neglect resistance of wire

2 Answers   L&T,


why we connect dg neutral with ground?

1 Answers  


can we use 3 phase UPS for Motors and Other Machines

4 Answers   ACC,


what is the function of avr when synchronous generator act as synchronous motor

1 Answers  


what is phantom load, Give any example

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)