For a certain load i need 100kw load ,In that case what
rating mccb should i use?
Answers were Sorted based on User's Feedback
Answer / chintan patel
It can be different for DC , 1phase AC , 3 phase AC , systems,
Lets calculate for all ,
1 ) For DC ( you have not mentioned Voltage but considering 230 V )
100 kw means 100000 watt
formula for DC power p= vi
100000= 230xi
i=100000/230= 434 amp
we always use current rating of the mccb is 1.5 times of full load current so we can use 434x1.5= 652 amp.
( if system is not running on full load select 630 Amp MCCB, if its on full load select 800A )
2 ) For 1phase AC,
Power: P = V I cos phi ( cos phi is power factor is not known assume 0.8 )
100000 W = 230 x I x 0.8
I = 543 Amp
we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 543 Amp X 1.5 = 815 Amp
select 800 Amp MCCB
3)
If load is 3 phase AC ,
Power P = sqrt(3) x V x I x cos phi
100000 w = 1.73 x 415 x I x 0.8
I = 174
we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 174 Amp X 1.5 = 261 Amp
( if system is not running on full load select 250 Amp MCCB,
if its on full load select 315 A )
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kalyan sharma
for 100 kw we will use 3 phase supply inplace of single
phase.
use formula p= 1.732 vi cosphi
100= 1.732*0.415*0.8*I
I = 174 amp
we always use current rating of the mccb is 1.5 times of
full load current so we can use 250 AMPs MCCB.3P/4P.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / rajat
for 100 kw means 100000watt
use formula p= vi
100000= 230xi
i=100000/230= 430 amp
we always use current rating of the mccb is 1.5 times of full load current so we can use 430x1.5= 645 amp
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / r g walia
for 100kw load required 630 amp mccb will be used.
| Is This Answer Correct ? | 2 Yes | 3 No |
Difference between on line capacitor and Station type capacitor.
application s to shunt coil
what is the meaning of 16/20 mva of transformer
what is mean by PIR in circuitbreaker and give me detail of that?
I have 30KW Motor Starter Panel, System voltage is 480V, So i have to convert voltage 480 to 220V to give the contactor coil. How i can select control transformer, Which rating transformer i can use this panel, what is the procedure, please tell me.
what is calculation mathod/formaulla for deciding Size of busbar (Copper/ aluminum)for L.T. panel on Various Fault level like 50kA,25kA,10kA
we all know that in capacitor there will be no ay physical connection between the two electrodes of the capacitor ,and the charge is stored between these electrodes during charging , so with out any physical connection how these charge is transferred from one plate to the another plate during the discharge?????
draw waveform of capacitor or inductor in a d.c ckt(during transient) with zero resistance with it(in series or parallel)also neglect resistance of wire
why we connect dg neutral with ground?
can we use 3 phase UPS for Motors and Other Machines
what is the function of avr when synchronous generator act as synchronous motor
what is phantom load, Give any example
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)