can we use 3 phase UPS for Motors and Other Machines
Answers were Sorted based on User's Feedback
Answer / engineered
Yes we can,
we have to ensure following things
1. In order to cope up with starting current of motor, we
have to select higher rating batteries, we can calculate
Idc required at starting of motor.
We have to refer battery current charts.
I have successfully run 3 nos. 7.5kw motor on 200kVA UPS
but when i tried to run single 7.5kW notor on 20 kVA ups it
failes to start.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / nilkanth tailor
yes....we can use...but for that we need high power IGBT
which can take load 3 phase motor....
i think that for 3phase UPS,we have to make 1phase to 3
phase converter...and suppose thier is no any electricity
thier then high current capacity battery will be needed coz
thier is 3phase so more power u need, this battery suppy is
given to 1 phse and it convert in to 3 phase by
converter...for that we use IGBT....and this 3 phase given
to the 3 phase motor...
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sms
Why not? Definitely, only U needs to decide proper rating
of UPS which will take care of Motor load which u want to
run on it.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / vaseekaran
We can use the UPS for the motors.but we have to select the correct rating of the load.while selecting we have to keep the time we required to load to run through ups.
| Is This Answer Correct ? | 1 Yes | 2 No |
During the transients in alternator,the mechanical power input remains almost constant while the electrical power output changes significantly.Why?
What is Ohms law?
28 Answers College School Exams Tests, KPTCL, L&T,
What is the significance of integral controller and derivative controller in a pid controller?
how to calculate the earth mat design in 132 kv substation yard ????
0 Answers Divis Laboratories, KSEB, SWPL,
why corona ring is used in out door switchyard lightning arrestor
Why the power factor of the alternator in power plant is kept .8 lagging. Can't we maintain it at 1.
I WANT TO know WHICH WAY IS BETTER FOR CONNECTION BETWEEN POWER TRANSFORMER AND MAIN DISTRIBUTION PANEL. 1-IS BETTER WE USE CABLE? 2-IS BETTER WE USE BUS DUCT? my transformer rate power is 2500KVA
what are the usual topology of transformers at different substations in the power system and why that particular topology is choosen. what are the limitaions of that topology?
sigal phase supply is 230 v ac two phase supply is 415 v ac why three phase supply is 415 v ac why not 690 v ac
the grid connection required for a 50 MegaWatt fotovoltaic powerplant is higher or lower than 35kv (high or medium tension)?
1.what is difference between line,neutral and earth 2.IF single phase voltage is 230v ac and what should be the voltage between line to neutral,neutral to earth and earth to line
how to modify DOL control panel into Delta Y connection?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)