Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


IF i have switchgear with busbar current rating of 1000Amp
35kA then is it necessary to have outgoing breaker kA rating
to be equal to busbar kA rating?

Answers were Sorted based on User's Feedback



IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / rajender mohan

The Busbar Rating specifies the maximum short circuit current it can see and operate, so you can put a breaker up to breaking capacity of busbar,
Ambience temprature has to taken into consideration while designing the LT Panel.

Is This Answer Correct ?    3 Yes 0 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / opselvaraj

Not neceesary but it is preferable to have the same rating
from operation/maintenance point of view.

Is This Answer Correct ?    4 Yes 2 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / anil jangra

KA rating of any switchgear is depending on fault level of connecting load,so it necessary to calculate the fault current of load than select the switchgear rating,as per my opinion the must be able to clear the fault without damaging it self and healty one feeder also.

Is This Answer Correct ?    0 Yes 0 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / pravin deshbhratar

yes, whatever fault current rating that we are maintaining
for the Incomer breaker same has to be maintained for
outgoing breaker also unless there is a stepdown
transformer in line. Because the fault level is calculated
on the basis of actual load of the substation that it is
going to carry out, so it is suggested that we have to use
the same KA ratiing for Incomer as well as the Outgoing
breaker.

Is This Answer Correct ?    1 Yes 4 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / mohammad farman khan

Not Necessary,depend upon your system means you are going
to use same KA rating for reactive power or normal power.if
you are using for reactive power then you hava to have same
KA rating of BB.however, you can check for normal load.

Is This Answer Correct ?    0 Yes 3 No

IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoi..

Answer / r.gunasekaran

Circuit breaker KA rating should be more than that bus bar
KA.

Is This Answer Correct ?    0 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

What is meant by power factor correction?

5 Answers   Aspire,


I am having a 42KW 3 phase electrical heating furnace, heating element is 80/20 nichrome material, my connections is made in such a way that 2 star connection compromising 2 coils per phase so totally 12 coils, shall if i use it unbalanced star condition (instead of 2 group of 3 phase or 1 group of 3 phase, connecting 4 phases of 5 phases) what will be the consequences and is it acceptable?

0 Answers  


in catridge heeter  watts =110, 260 v ,  i checked in multimeeter meeter shows 50 ohms but oms law r=v square /w  260*260=67600, and 67600/110=614.5 ohms  how to caluclate exact ohms in heetre s 

2 Answers  


Details about Flux Compensated magnetic Amplifer starter for motors

0 Answers  


what is the function of statics switch in ups and tell me parts

0 Answers   Dalkia,


Can Anyone suggest the Standards (IEC or IS) for selecting copper current density?

0 Answers  


how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!

0 Answers   SRES,


Why DG set rating in KVA

13 Answers   Crompton Greaves,


Is it possible to increasing the real power generation by reducing the reactive power in power generation plants

3 Answers  


Is it reuired to use house service barcket for 31/2 core 300 Sq.mm cable,if the distance between pole & shop is around 2 mtrs only or can I hang the cable with GI support in air? upto what size of cable GI serrvice btacket is necessary?

1 Answers   HAL,


How do the synchronizing lamps indicate the correctness of phase sequence between existing and incoming alternators?

0 Answers   VECL,


It is advisable 2 use auto-transformer if transformation ratio is-a)110KV/11KV,b)230kv/110kv,c)110kv/66kv,d) 400kv/230kv

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)