a 3 phase slip ring induction motor is wound for 4 poles on
stator and 6 poles on rotor; when 3 phase balanced voltage
source at 50 hz is applied to motor it will run at
a)1500rpm b)1000rpm c)750 rpm d)zero rpm
Answers were Sorted based on User's Feedback
Answer / pramit dutta
i think the question is incomplete ,
we know n=(1-s)ns , so, ns=(120*50)/4=1500 rpm.
so we need to know the slip of motor then we find answer.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / lolipop
Answer is d.) as it looks more nicer and more lengthy
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / netserab
first v 120f/p i.e. when 120 constant
f given ferquency
p is number of poles
then we have 4 poles on the sator and 6 poles on the
roter 120x50/3/2=1000
| Is This Answer Correct ? | 1 Yes | 3 No |
how we can improve P.F. by using capacitors ?
how system fault level is calculated?
what is the difference between PLC and embedded system
why we use negative feedback in control system.
Electricty is generated at around 16kV, then step up to 220kV for transmission then steped down to power transformers then DTs and then through the LT n/w it reaches the consumer end. At the consumer end 230V supply is required. So, why is electricity not generated directly at 230V and transmitted?
What is the difference between KW & KVA ?
What is voltage ratio of a transformer?
i want to syncronise 5 nos of DG. How? pls reply
in single phase circuit if i connect a heater between phase and neutral, then what will be the current path? phase to neutral or neutral to phase.
A group of machines (wind turbines) connected with 33KV feeder and each machines are having individual VCB. The 33KV feeder connected with 110KV/33KV substation. The 33KV feeder tripped by over current at Substation and fault recorded at Substation as OC-R&Y phase. Same time the group of machines VCB tripped by over voltage, the fault recorded voltage was above 66KV by numerical Under/Over voltage relay. While grid drop time, this much of voltage hike is possible?
RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV is ok ,but haw to calculate the KA rating?
What, in the construction of a transformer, controls KVA? For example 600/208/120 V transformer can be 10kVA or 45kVA!!! What do we change in the construction of a Transformer in order to change the rating but not the voltage.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)