Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Can we operate a DG Set in paralell with Transformer ?

Answers were Sorted based on User's Feedback



Can we operate a DG Set in paralell with Transformer ?..

Answer / ekanadam naik

yes we ca operate dg set with transfer but voltage and
freqency must be matched, with help of PLC,

Is This Answer Correct ?    20 Yes 3 No

Can we operate a DG Set in paralell with Transformer ?..

Answer / a. venkatesh

All the power source it may be transformer or Alternator
(DG-DC power generator).
For parellel operation synchronisation is important. I.E
Voltage level, frequency, phase angle should be equal for
the both sources.

For checking the synchronisation previously DARK LAMP
METHOD was used. Now a days special relays used for this
purpose. Relays MES 120(Schneider), 7UT relays in Siemens.

Is This Answer Correct ?    4 Yes 0 No

Can we operate a DG Set in paralell with Transformer ?..

Answer / sangram

yes, we can Theoretically do it. we want to use aditional
relay and some equipments like Reversepower relay, DF/DT.

Is This Answer Correct ?    2 Yes 0 No

Can we operate a DG Set in paralell with Transformer ?..

Answer / meka sekhar

theoretically DG can be operated parallelly with
transformer as long as voltage, frequqncy, phase angle are
within limits. However, in industrial practice, only
momentarily paralleling will be done between DG &
transformer. Sometimes if they want to check loading of DG,
it can be paralled with transformer so that it will not
affect loads which are connected to bus.

Is This Answer Correct ?    0 Yes 0 No

Can we operate a DG Set in paralell with Transformer ?..

Answer / sangram patil

Yes, called as synchronizsation of DG & EB of both. for
this parallel operation we want to concentrate on Voltage,
Frequency & Phase angle of both of equal.
and for Auto loading & Autobalancing we want to use
Woodward, C&S OR scnhider make relay.

Is This Answer Correct ?    0 Yes 1 No

Can we operate a DG Set in paralell with Transformer ?..

Answer / ram

no dg set can not be connected with x-mer DG can not give
constant freq.

Is This Answer Correct ?    2 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

My system is 22kv/3.3kv transformer. client is asking to use NGR, but as we have dedicated Neutral Earthing systems which has a value less than 1 Ohm. So i want solid comparision. Why i should not use NGR as my system is already protected.Can any one help me to get out of this.how should i reply on basis of some great comparision and calculations. Please help

2 Answers   Ariel,


How can I known multiplying factor .without multiplying table

0 Answers   Student,


what is the reason the main breaker is trip during the motor is running? (some time the breaker is not trip)

0 Answers  


What is differance betwwen Conventional MCC & Inteligent MCC?

2 Answers   Quantum, Siemens,


what is general test conduted by transformer

8 Answers   Wipro,


What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.

0 Answers  


Dear All, In a 400V power system, ratio of three current transformers installed incoming switchgear is 4000/1. Maximum three phases short circuit current of this system is 48kA. One CT is installed on neutral of upstream transformer (6/0.42kV, solidly earthed) for 51G protection. Would you please inform me about the correct CT ratio of this current transformer (on neutral)?? Thanks a million

2 Answers  


what is the use of power factor ? where its applicable ?

4 Answers  


Which type of control system is expensive — closed loop or open loop?

1 Answers   GE,


what is LOS(line of sight)?

1 Answers  


3.The slip of an IM UNDER FL condition is about.....

1 Answers   SSC,


what is the unit of electricity????????????

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)