Can we operate a DG Set in paralell with Transformer ?
Answers were Sorted based on User's Feedback
Answer / ekanadam naik
yes we ca operate dg set with transfer but voltage and
freqency must be matched, with help of PLC,
| Is This Answer Correct ? | 20 Yes | 3 No |
Answer / a. venkatesh
All the power source it may be transformer or Alternator
(DG-DC power generator).
For parellel operation synchronisation is important. I.E
Voltage level, frequency, phase angle should be equal for
the both sources.
For checking the synchronisation previously DARK LAMP
METHOD was used. Now a days special relays used for this
purpose. Relays MES 120(Schneider), 7UT relays in Siemens.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sangram
yes, we can Theoretically do it. we want to use aditional
relay and some equipments like Reversepower relay, DF/DT.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / meka sekhar
theoretically DG can be operated parallelly with
transformer as long as voltage, frequqncy, phase angle are
within limits. However, in industrial practice, only
momentarily paralleling will be done between DG &
transformer. Sometimes if they want to check loading of DG,
it can be paralled with transformer so that it will not
affect loads which are connected to bus.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sangram patil
Yes, called as synchronizsation of DG & EB of both. for
this parallel operation we want to concentrate on Voltage,
Frequency & Phase angle of both of equal.
and for Auto loading & Autobalancing we want to use
Woodward, C&S OR scnhider make relay.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ram
no dg set can not be connected with x-mer DG can not give
constant freq.
| Is This Answer Correct ? | 2 Yes | 9 No |
hi... Can anybody give me description of type-2 coordination, IP protection, NEMA standards ? Thanks..
pleasee tell me the risks and hazards of a Cable Jointer job? Thank you.
what is nuetral grounding
What is the material used for the core of a high freiquency transformer?
How does a diesel generator works?
Why the generator rating in kva
32 Answers CompuCom, DLF, Genpact, HNG, SIPM,
What kind of preventive maintenance are there for AC generator?
We have one Energy meter for Measuring the voltage,current,power,energy(KWH,KVARH,KVAH) & power factor.The problem is that the meter does not show whether the PF is lagging or leading.So i want to know that is there any way or calculation to find out that whether the PF sign (lagging or leading) depending upon the above mentioned parameters?
What is best method of Calculating Short Circuit current in power system network.
Its possible to use 3core 2R of 240 sq.mm cable for 3phases & separely 50sq.mm 3core cable fully for Neutral for connection of PCC to MCC 3ph..4wire system?
how we decide scurt (disc) of insulator with respect to kv rating
how can we check the earth resistance
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)