Can we operate a DG Set in paralell with Transformer ?
Answers were Sorted based on User's Feedback
Answer / ekanadam naik
yes we ca operate dg set with transfer but voltage and
freqency must be matched, with help of PLC,
| Is This Answer Correct ? | 20 Yes | 3 No |
Answer / a. venkatesh
All the power source it may be transformer or Alternator
(DG-DC power generator).
For parellel operation synchronisation is important. I.E
Voltage level, frequency, phase angle should be equal for
the both sources.
For checking the synchronisation previously DARK LAMP
METHOD was used. Now a days special relays used for this
purpose. Relays MES 120(Schneider), 7UT relays in Siemens.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sangram
yes, we can Theoretically do it. we want to use aditional
relay and some equipments like Reversepower relay, DF/DT.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / meka sekhar
theoretically DG can be operated parallelly with
transformer as long as voltage, frequqncy, phase angle are
within limits. However, in industrial practice, only
momentarily paralleling will be done between DG &
transformer. Sometimes if they want to check loading of DG,
it can be paralled with transformer so that it will not
affect loads which are connected to bus.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sangram patil
Yes, called as synchronizsation of DG & EB of both. for
this parallel operation we want to concentrate on Voltage,
Frequency & Phase angle of both of equal.
and for Auto loading & Autobalancing we want to use
Woodward, C&S OR scnhider make relay.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ram
no dg set can not be connected with x-mer DG can not give
constant freq.
| Is This Answer Correct ? | 2 Yes | 9 No |
why electron flow is opposite to current flow?
Detailed working of a diesel generator set ?
1 Answers Airtel, Honda, Kirloskar,
what happens if the phase sequence of parrlel connected sys will changed & phase displacement
what is the meaning of impedance protected in instrument cooling fan
why there is a high voltage line in multiplication of 11?i.e.- -66kv,11,kv,22kv
How is the Depth of Stator Slot being calculated for Synchronous Generator?
why we are calculating the capacitance between phase(conductor line)and ground in transmission line?why cant we calculate capacitance between the phase and the nuetral line?if so what is procedure.
Give me check-list for electrical preventive maintenance of machine tool.
solar energy light efficiency & disadvantages?
why nearly all voltages are in the multiples of 11?
I'm looking for a mnaual set for a Teradyne J750. Softcopy would be preferred but I'll take what I can get.
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)