Can we operate a DG Set in paralell with Transformer ?
Answer Posted / a. venkatesh
All the power source it may be transformer or Alternator
(DG-DC power generator).
For parellel operation synchronisation is important. I.E
Voltage level, frequency, phase angle should be equal for
the both sources.
For checking the synchronisation previously DARK LAMP
METHOD was used. Now a days special relays used for this
purpose. Relays MES 120(Schneider), 7UT relays in Siemens.
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers
how power trnafor from 1 point to another point in bus bar ya transmission line( voltage trnasfer from 1 point to another poin)
what is the purpose of bypass mode in energy lighting transformer?
How to find ampere on ht side for selection of cable size ???
How is the percentage impedence of a transformer fixed at design stage???
What is meant by celling voltage & current in excitor ?
Explain mechanical rotational system?
in Telecom DC system-why positive +ve is made earthed.and - ve is fed to load.
How to determine the breaking capacity such as break down current and break down voltage for VCB and CT's.
1. What is differential relay? How it operates? 2.How to calculate the Short Circuit Impedance in Transformer? 3.What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works? 4. While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply? 5. What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer? 6. Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example? 7. Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient? 8. What should be the minimum and maximum ohmic value for earthing? 9. Why DC Currents are not used in transformer? 10. What is the Frequency while we step up the voltage from 220V to 11KV? Is it possible? Explain it?
tell me some type of questions throught which i can prepare for exam and do my best
What is step signal?
The screw thread commonly used for transmission of motion is one of the following types of threads
I have a current transformer with 1 main reading meter with transformer outside the building and a control panel having 5 CT reading meters with black round coils inside the building. I want to know, A) when current pass through the Transformers, will the current be reduced or be the same and after that B) when current pass through the CT meters with black round coils, will the current be reduced or be the same. C) in the above process will the reading of the main meter be same or different, from the total reading of all the 5 CT meters.
How to decide and select the different earthing wire size for the different types of earthing
What is mean by hot and cold loop testing?