Dear All,
In a 400V power system, ratio of three current transformers
installed incoming switchgear is 4000/1. Maximum three
phases short circuit current of this system is 48kA. One CT
is installed on neutral of upstream transformer (6/0.42kV,
solidly earthed) for 51G protection. Would you please inform
me about the correct CT ratio of this current transformer
(on neutral)??
Thanks a million
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The maximum earth fault current occurs when the phase comes
in contact with the earthed metal part.That will be about
230/0.5 i.e. about 500 A ,ignoring impedance of tr and
taking ER as 0.5 ohms.It is the usual practice to set EFR at
20% of OCR setting.For REFR the CT ratio should be the same
as that of phases.You can have a 2 core 4000:1 NCT and set
the 51G at 0.1 to 0.2 In ,using one of the two secondaries.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
Further you can not expect much earth fault current in
neutral earthing as the voltage is only 230.Unless the phase
comes in contact with earthed metal part or welding is done
on the ground, this current will be too low to be picked up
by ct.As the power supply points are provided with fuses
,the relay may not get a chance to act at all.
Is This Answer Correct ? | 0 Yes | 0 No |
when turbine trips generator will becomes induction motor or synchronous motor?
What is Star Delta Connection, where it is applied & what for it is used
4 Answers Premium Transmission,
how do we calculate of transformer in va?what is calculation?
what is the function of potential transformer in s/s
what is the exact meaning of power
state the functions of different parts of star delta starter.
What happen if 200KVAR capacitor continuesly connected to load and all the plant machinaries are not in working?
Why do we use copper cable for HT Supply and why not Aluminium?
WHAT IS counter flux IN CT?
In n high voltage 11kv system What happened if 1 of CT cable (IDMT) loose.Will e/f or o/c trip.please explain detail
What is the approximate percentage of Si content in transformer core(CRGO-Cold Rolled Grain Oriented)? Why it is kept so low?