What are protection of transformer on HT side & on LT side?
Answers were Sorted based on User's Feedback
Answer / santosh mulay
For HT tran. high winding & oil temp. alarm with triping
portection must be there. And Buchholz relay triping also
necessary. Addition to that Over current, earth fault realy
must be there.
| Is This Answer Correct ? | 9 Yes | 2 No |
HT
Overvtg/undervtg, Earth fault,Surge protection, differential protection
LT
Undervtg, REF protection,Buccholz relay, sudden pressure relay, Overcurrent protection.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / krishna
If the transformer is below 1000KVA, for the HT side
protection AB switch and HG Fuse must be used and for the LT
side protection ACB/OCB must be used.
If the transformer is above 1000KVA, for the HT side
protection VCB/ACB must be used and for the LT side
protection ACB/OCB must be used.
| Is This Answer Correct ? | 11 Yes | 14 No |
Answer / neeraj dubey
on ht side Drop out fuse used for overhead line and lt sie
HRC fuse with fsp ( Fuse section Pillar)
| Is This Answer Correct ? | 1 Yes | 7 No |
Is Softbitonline HT Transformer Design Software is AutoCAD compatible?
why neutral busbar size is half of the phase busbar size in control panels
where we sense the fault from the transmission lines?any operation example for distance relay?rear panel connection for this relay?
why transmission line 11Kv OR 33KV,66Kv not in 10kv 20kv?
43 Answers A2Z Group, Baiji Power Plant Gas, Electrical, HCL, Kirloskar, Mepco, NEPC, OAMC, UNI, University of Lahore,
What is negative phase sequence?
7 Answers Hindalco, Universal Associate,
WHAT WILL BE THE SPEED OF MOTOR IF NO.OF POLES ON STATOR ARE NOT EQUAL TO NO. OF POLES ON ROTOR.???
what is the merz prodution ? what is the turn to turn fault?
why insulators are colured in brown only?
How current is reduced in STAR connection?
We have a 1275KVA existing Transformer in a power plant project. Customer want to get it test & confirm whether it is a Dyn1 Transformer or not. Pleae let me know how to test it.
why in isolation transformer we dont get any shok?
Can 4pole (3 phase+neautral )RCCB proper functioning in only 3 phase load (no neautral, no Earth) ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)