What is the different between buchholz relay and pressure
relief device?
Answers were Sorted based on User's Feedback
Answer / markandeya
bucholz relay will bi instaald in between conservator and
transformer body.
it will give trip command when flow of oil is high or no
oil in conservator.
PRV is connected at the top of atransformer body. it will
opens towards atmospare when inside pressure is high
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / rupesh birla
Baccho relay genral operated through gas actuated in transformer. And prv relay operated throw oil pressure in transformer.
| Is This Answer Correct ? | 2 Yes | 4 No |
what is saturation kit?which use above 15 kw motors panel side.
Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!
What is the winding resistsnce need to be in a 1000kva, 11kv/415v transformer, between ht winding to lt winding, ht winding to earth, lt winding to earth.?
In 3phase supply Voltage will come around 370v then what will happen?(mean what will effect on electrical equipment like AC,UPS,Motors.)
why do we prefer a 3-phase delta connected load rather than star connected?
an ac induction motor gets overheated when operated at a low frequency of 25 hz a instead of 50 hz. reason?
what is vA rating and class of a ct.
what is rotary ups?
how to convert the KVAR to microfarad??????????????????
what is derating?, why it is neccesary, it is same for all means for drives, motors,and cables.
how brushed dc motor operating ?
what is mind in cable
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)