1.what is use of isolation transformer.
2.Differance between KWH,KVAH,KVARH,KVA.
3.Main use of the CT and PT.
Answer / bilal hamad
1- to isolate supply and load in case of faults and power harmonics (to protect the source) and also to protect the load .
2-KWH: the real power (useful) consumption per hour.
KVAH: the total power consumption per hour.
KVA: the total power (real and imaginary)(vectors sum).
KVARH: the imaginary power consumption per hour.
in summary: the power factor will control the amount of real (active)power and reactive power. all real loads are usually inductive loads or resistive, this will reduce the power factor and then increase the reactive power, the solution is to install capacitor banks to increase the power factor and then reduce the reactive power so increase the active power.
3. CT: is a step down current transformer used for current measurement and protection.
PT or VT: is a step down voltage transformer used for voltage measurement.
| Is This Answer Correct ? | 9 Yes | 1 No |
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
for 500mw power production how many range of transformer set in unit please reply if three transformer use .
any body,pls tell me how to done relay coordination ? how to coordinate by TCC curve?how to read the tcc curve?
what s the differenc between electrical &electronis , how to define them
how do we select a copper power cable for a 10 HP, 1440 rpm, 440V, 3 phase AC motor?
why normally Generator rating are between 11Kv to 22Kv?
Why power factor is arising in electrical circuit, is it possible to eliminate from the circuit, why
why pull the single core cable?
if 2 coil of 1000W connect in series and 200 v is applied across it . then what is the total power of coil when coil have only resistive load .
When PRV operated at power transformer ,can anybody tell me particular pressure for 50mva transformer plzzz.
What is stub protection is all about?
if dc motor can operate by ac supply ? if its possible means how ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)