Why we use Y-Y connection in power transformer (8-10 MVA,
132 kV to 11 KV)and D-y in distribution transformer (2 MVA,
11 KV to 440 Volts)?
Answers were Sorted based on User's Feedback
Answer / rajesh kumar
we use y-y conection in exctra high voltage transformer
like 132kv as we know that in star connection line voltage
is-1.732.phase voltage.so less insulation required in y-y
conection.
in distrubution transformer at 11kv we can easily insulate
windings due to voltage level is low.and also get domestic
load.
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / rajesh kumar
we use y-y connection in power transformer 132kv as we know
that in star connection line voltage is-1.732.phase
voltage.so it is easy to insulate the winding as the
voltage level is low.and cost is less due to degrading of
insulation.
Is This Answer Correct ? | 3 Yes | 0 No |
ok u r using any transformer , anywhere but
the important is what is ur need ?
if u want , in distribution u need 440v -phase to neutral
u r using star connection
u need 11kv hv , u use delta connection
the important is u r using neutral or not generally line
side transformer has delta connected
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / morongoa
WE USE Y-Y CONNECTION IN POWER TRANSFORMER COS WE NEED STAR
POINT SO IN DELTA YOU DNT HAVE A STAR POINT AND FOR
DISTRIBUTION YOU USE D-Y CO YOU TAKING POWER FRM SUBSTATION
WHICH IS 11KV FRM SUB TRANSFORMER TO YOUR CONSUMERS
Is This Answer Correct ? | 1 Yes | 8 No |
Does the dg syncronization sucessful in practical.
explain the types of drives
why industry prefer ht motor instead of lt motor.
What is thermal overload relay
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
the max. power will be transferred if …… a) sending end vol. is high b) receiving end v is high c)…….. d) corona loss is least
2 Answers Engineers India Limited,
Alternator rotor earth fault relay circuit
1hp single phase load = howmuch 3 phase load
How to select Main CB Rating for 187 KW Load?
Between educational qualification and practical work experience, give us a brief explanation on your practical experience in your past Endeavour that you performed well to the satisfaction of your past or present employer?
. Why the transmission lines are in 11kV, 22kV, 33kv, and why not 10kV, 20kV, 30kV?
in case dc we mark as + ve & -ve..but in case a.c. we mark as ph&N...Y LIKE PLZ TELL ME