Why we use Y-Y connection in power transformer (8-10 MVA,
132 kV to 11 KV)and D-y in distribution transformer (2 MVA,
11 KV to 440 Volts)?
Answers were Sorted based on User's Feedback
Answer / rajesh kumar
we use y-y conection in exctra high voltage transformer
like 132kv as we know that in star connection line voltage
is-1.732.phase voltage.so less insulation required in y-y
conection.
in distrubution transformer at 11kv we can easily insulate
windings due to voltage level is low.and also get domestic
load.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / rajesh kumar
we use y-y connection in power transformer 132kv as we know
that in star connection line voltage is-1.732.phase
voltage.so it is easy to insulate the winding as the
voltage level is low.and cost is less due to degrading of
insulation.
| Is This Answer Correct ? | 3 Yes | 0 No |
ok u r using any transformer , anywhere but
the important is what is ur need ?
if u want , in distribution u need 440v -phase to neutral
u r using star connection
u need 11kv hv , u use delta connection
the important is u r using neutral or not generally line
side transformer has delta connected
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / morongoa
WE USE Y-Y CONNECTION IN POWER TRANSFORMER COS WE NEED STAR
POINT SO IN DELTA YOU DNT HAVE A STAR POINT AND FOR
DISTRIBUTION YOU USE D-Y CO YOU TAKING POWER FRM SUBSTATION
WHICH IS 11KV FRM SUB TRANSFORMER TO YOUR CONSUMERS
| Is This Answer Correct ? | 1 Yes | 8 No |
hi friends how 3 phase converter functioning ?what is working principle of rotory phase converter ?
what is the method of electric earth for the protection of low voltage electric equipment
1 Answers MacLellan, Shiva Corporation, Siemens,
why DG,Transformer,UPS capacity will be tell in KVA but not in KW?
could anyone suggest project title
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
Amoung all classes of electric machines, why the transformer uses oil as one medium of cooling?
it is possible to run 130V AC and 230 V AC cables run in same tray
how do you reduce the skin effect
Do closed loop systems require manual input?
100 MVA 3-phase alternator with earthed neutral has a reactance of 5 ohms per phase. what will be the fault MVA of generator.
Name quantities which are not transformed in the tranformer.
What are the symptoms of a bad PG card of a drive (inverter) esp. of Yaskawa Ac Drives (inverters) G7 ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)