What are the protections used in a HT breaker to protect
the HT motors.
Answers were Sorted based on User's Feedback
Answer / shantanu dash
To protect the HT Motor, Motor protection Relay with the
following protection features are used in HT Breaker. they
are :-
1.Short Circuit
2.Excessive Start time
3.Thermal Overload
4.Locked Rotor during running/start up
5.Unbalance/loss of Phase/single phasing
6.Earth fault
7.Loss of Load
8.Temperature supervision of motor
9.Limitation of No. of Starts/Time between starts
Is This Answer Correct ? | 33 Yes | 3 No |
Answer / sivaraman
We have to use for Motor Protection Relay (SPAM 150C)
1.Short Circuit
2.Excessive Start time
3.Thermal Overload
4.Locked Rotor during running/start up
5.Unbalance/loss of Phase/single phasing
6.Earth fault
7.Loss of Load
8.Temperature supervision of motor
9.Limitation of No. of Starts/Time between starts
All above facilities are available in this relay.
Is This Answer Correct ? | 27 Yes | 2 No |
why we use REF and Differential Protection in one transformers?my doubt is both protections are operated in internal fault only.why we want to use 2 protections?please clarify.
Which oil is used in Transformer?
Circuit diagram of tube light without starter using electrical choke
Hi,i want to appear for IES (EEE),can any one plz help me how to apply and how to prepare
length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?
Tell me about ur past electrical maintanence job
0 Answers Apollo Power, Solar,
What is meaning of Float Charging of Batteries???
what is skin effect and why is it absent in DC systems
How to connect frequency meter in metering circuit?(single phase and three phase frequency meter)
can we start mulitple 3 phase induction motors with common starter?
Why not instal the NGR in 11kv/433kv trasformer?
why ups rated in kva