Answer / v. senthilkumar - skpcl

Fully Automatic Star-Delta: In these starts Start-Delta
operation is an automatic one, which is accomplished with a
Timer fitted inside the starter. The time period from Star
to Delta can be adjusted between 7 to 15 sec. The Starter is
provided with Bimetallic Thermal Relay for protection
against Overloading & Single Phasing Conditions.

Semi-Automatic Star-Delta: These Starters are operated with
3-push button systems, in which the third push button
(Yellow) is used to change the motor running sequence from
Star to Delta. Bimetallic thermal overload Relay is fitted
in these starters for protection against overloading and
Single Phasing problems.

Is This Answer Correct ?    30 Yes 2 No

What is the difference between automatic & semi-automatic star-delta starters?..

Answer / seimence

the difference between automatic & semi automatic starter
delta starters becouse the star delta starters are both use
in automatic & semi automatic condition so automatic
starters are work in automatic this not oparete manuali but
the semi automatic starters both are manuali & automatic
performe in ac machine.

Is This Answer Correct ?    11 Yes 6 No

What is the difference between automatic & semi-automatic star-delta starters?..

Answer / prabhakar

Semi automatic starters will be opreated manouly which will
trip only on high voltage

fully atomatic starters will work with level
control ,timers and single phase priventers so it is fully
automatic

Is This Answer Correct ?    8 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

Size of the power cable like 1.5,2.5,4 sq.mm which area calculated from whick area or how specified the size?

1 Answers   MRF,


What is the basic difference between the electrical engineering and electronic engineering?

4 Answers  


What is the meaning of BUS?

20 Answers   CII, KLG Systel,


What is the lower limit of break-down voltage of converter transformer.

0 Answers   Tata Steel Limited,


what is fuction static switch in ups and tell me use parts name and fucion

3 Answers   Dalkia,






at the time of starting back emf of a motor is zero.so how can it will start to run??

1 Answers  


why is the core of the underground cable is spiral in shape instead of straight?

8 Answers   Mecon,


I AM FROM ELECTRICAL ENGINEERING ? I AM ASPIRING FOR "BHEL".HOW I HAVE TO PREPARE .ON WHICH TOPICS TO BE CONCENTRATE MORE.PLEASE GIVE FULL DETAILS OF WRITTEN EXAM.

0 Answers   Bhel,


On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Current: 693A Voltage:294/20KV OLTC Type: T III Y1000 110/c 12193w Max Operation Current: 295A Step Voltage: 550V Arrangement in Tx windings: Y Connection Problem: Damage of Unit 1 Generator Transformer On Load Tap Changer (OLTC) Description of Incident: 9.00 a.m. :- Generator No Load test on excitation system started 10.30 a.m :- Carried out AVR change over test 11.30 a.m :- Preparation for Generator Manual Synchronizing test 12.00 a.m :- Manual Synshronizing test started. Observed incoming generator voltage higher than running voltage. CECR operator operated Generator Transformer OLTC to bring down the incoming generator voltage 12.03 a.m :-Generator Transformer abnormal alarm operated at Gen.Control Desk (CECR) CECR operater at Generator transformer bay informed that the transformer oil splashed out from OLTC. CECR operater informed that he heard explosion inside OLTC. Observed Oil level & Oil Flow alaram operated at Tranformer local annunciator. 12.05 am :- CECR operator 'Open Gen Field Breaker” 12.10 a.m. :- Elec1 team inspected the OLTC and found the OLTC rupture disk was broken and oil spilled at OLTC area. - Elec1 found the OLTC top cover bulging. Do anyone know why and possibility cause happen in this OLTC.

9 Answers  


200-100/1-1A – Transformer Knee point voltage

1 Answers   AAPT,


What are the difference between off-load tap changer and on-load tap changer in transformer?

2 Answers   HCL,


What iz main protection of mediuum voltage motors and what iz the standard IR voltage of 6.6 and 11kv motors.

1 Answers   GE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)