What type of tranformer generaly at soft wares like
capacity 2000 kva 1800 kva etc iam confused it CT or PT
OR distribution tranformer
Answers were Sorted based on User's Feedback
Answer / ankit
Actually you are confused in the ratings:
A CT i.e. current transformer is used as an instrument
transformer to measure current.
And Similarly PT i.e. Potential Transformer is used for
voltage measurement.
The ratings specified by u are the nominal ratings of a big
building like Mall, IT park so the transformer is A
DISTRIBUTION X-MER which is used for meeting the load
requirements of that premise.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / manju & raju
Generally used for distribution Transformer.
CT-used for current measuring purpose.
PT-used for voltage measuring purpose.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / pawan dahiya
CT is current transformer and used in high current
PT is Potential Transformer and used in high voltage
Is This Answer Correct ? | 0 Yes | 3 No |
Which type of power plant is more easier to produce electrical power at economical condition?
what is tha online tapping and offline tappchange? which side connected primary or secondary and explain ?
what is the difference between electrical & electronics
245 Answers Axon Constructions, Banking, GDA Technologies, Infosys, MBA, Satyam, Satyam Tech, Snow White, TCS,
I have an 15A fuse MCB that controls a night storage heater. It needs replacing and is now obsolete. Is a 16A C curve MCB the correct replacement?
If one ct is reversely connected in Y system what will effect in kwh and kvarh meter?
How we calculate the Multiplying Factor of Kwh meter for 3 phase alternator.
how do i commission a distribution transformer knowing all its ratings and transformation ratios?d
Equal resistance of 100ohm each are connected to the arms of whestons bridge, which is supplied by 2v battery. The galvanometer can sense a current low as 1microAmp. What is the smallest resistance that can be measered.
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<
What is the Good Earth resistance value of G.I & Cu. Chemical Earthing & Normal Pipe Earthing?
0 Answers ABC, Reliance Life Sciences, TCS,
hai...... tis is Hemanth. jst now completed electrical engineering... i wanna to apper for ap tranco exam... plzz send me the previous q's paper link......thanx in advance.
IN A HT CABLES i.e. 1.9/3/3 kv, what is the meaning of 1.9 and 3.3.