What could be the problem if two power transformers trip on
stand by earth fault at same time
Answer / k.prakashchandra
If the point ct neutral earthing is in the path of earth
fault current, there is likelihood of tripping of standby
transformers on earth fault.
Is This Answer Correct ? | 1 Yes | 0 No |
Why the Motor takes High Current in Starting time?
What is the angle of inclination for the oil connection from transformer conservator to Bucholz relay and why?
0 Answers Alam Group of Companies,
differance b|w ground, neutral&earth
what is ground clearence in transmission system.is it varies wit conductor size,height of poles,span.
What quedtion to ask a electrical maintenance technician?
5 Answers Bhel, Royal Furnishers,
DESCRIBEPNEUMATIC SYSTM OF ASH HANDLING PLANT
avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid after synchronisation it regulates power factor why....
I WANT TO know WHICH WAY IS BETTER FOR CONNECTION BETWEEN POWER TRANSFORMER AND MAIN DISTRIBUTION PANEL. 1-IS BETTER WE USE CABLE? 2-IS BETTER WE USE BUS DUCT? my transformer rate power is 2500KVA
in cvt,there are two windings,1a,1n and 2a,2n.in my one project i use only one winding i.e.1a,1n. the other winding is not in use, so i connect it in open delta and want to close it by ibsertibg thermal resistor. the output of cvt is 132kv/115/sqrt3. plesae tell me exact value of resistor, so i may close it to avoid the resonance phenomenin. send me answer on this email adress please. aetcon-po@aetcon.com
Name a govt approved university which have 100% online engineering course.
how you taken aotitude test
The iron loss in a 100kva transformer is 1 kw and full load copper losses are 2 kw, then what is maximum efficiency occure at a load?