ups and invertor battery selection chart and full formula
Answers were Sorted based on User's Feedback
Answer / thowsif_emerson_csm team
UPS Battery Cacl:-
BATTERY RATING CALCULATION:-
The formula employed rating calculation is as stipulated
below :-
FORMULA EMPLOYED :
DC Current X Duration in Hrs
Capacity of Battery ( AH )=%age capacity utilization
UPS(KVA) x 1000 x Load Power Factor (=1)
Where , DC Current=Inverter efficiency x End Voltage
Hence , VAH = AH x Nominal Voltage
For e.g. : for 3 KVA UPS , 1 hour Backup :
3 x 1000 x 1
DC Current= 17.0 A
0.93 x 10.5 x 18
17.0 x 1.0
Battery ”AH “ = 27.4 AH
0.62
Hence , 18 nos of 12V/28AH batteries will suffice .
TOTAL VAH = 18 x 12 x 28 = 6048 VAH
The following assumptions have been made in the above
calculations :-
1. DC Voltage – 216 for 3 KVA
2. End cell voltage / battery of 10.5 V
3. Load Power Factor = 1.0
4. Inverter efficiency = 93%
% Capacity utilization is :
Duration % Capacity utilization
½ hr (30 mins) 52%
1hrs 62%
2hrs 74%
3hrs 83%
4hr 85%
For ups and invertor battery selection chart lOG On to:-
http://www.sharanapower.com/selection2.htm
| Is This Answer Correct ? | 22 Yes | 10 No |
please tell me, how i clear the objective test? when i studied form the one book after i solved the objective ,that time i solved that qes. but if i tried solve objective form the other book then i could not solved these que.
How can we estimate Gen rotor current?
will there be any problem by recovering slip from single phase induction motors?
Is HT capacitor rating connected directly to motor terminals , related to motor no load current?
An AC Motor to give DC supply what happen the motor.whats the problem are create.
transformers? power factor? machiences?
On the secondary side of a distribution transformer, we use 1c x 630 sq mm cable. Why dont we use 4 core cables instead of 1 core cables on the secondary. Why we use aluminium cable glands on the outgoing instead of brass cable glands?
What are the functions of temperature scanner in power transformer?
why the field winding in dc motor is not short circuited eventhough dc supply is applied across the winding
how to calculate the knee point voltage of current transformer?
in three phase 11kv transformer (11kv/433v) input( R,Y,B) output (X,Y,Z,N) the connection as follows 1 phase R -open 2phase y connected to both R and y of input] 3phase B- B what is the output voltage X to N ,Y to N , Z to N
how to make an earthing certificate
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)