how to calculate the input current in singel phase and
3phase supply to 5kva ups
Answer / h s dhillon
Let the supply is 3 ph 4 w having line voltage 400 volts
and phase voltage 230 volts,then:
in case of single phase:
I=5000/230=21.74 Amp
In case of 3 phase:
I=5000/Under root3 i.e.1.732x400
=7.22 Amp
Is This Answer Correct ? | 7 Yes | 2 No |
Why do you use an isolator on both sides of the circuit breaker? ( shortly answer)
WHAT MEANT BY SEVICE FOCTOR?
How do you change an AC motor to DC? why there is only 50 Hz frequency in india & not other?
Why a Transformer Noise during its running condition ??
what is skin effect?
Slip at maximum torque depends on A rotor resistance and reactance B stator reactance C load current D stator resistance
we have 3.5MVA-11/6KV transformer. how can we calculate earth fault current and NGR calculation?
what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?
why battery dc voltage become Half when we check with respect to ground for example 120volts + and - terminals and when we check + terminal with Earth thats 60volts why 60volts we can not ground the battery.
what are safety measures in /control in diesal engine/ explain them?
i need previous entrence exam papers of nhpc.
which subject is better to tell when hr asks the area of interest?..