ups and invertor battery selection chart and full formula
Answer Posted / thowsif_emerson_csm team
UPS Battery Cacl:-
BATTERY RATING CALCULATION:-
The formula employed rating calculation is as stipulated
below :-
FORMULA EMPLOYED :
DC Current X Duration in Hrs
Capacity of Battery ( AH )=%age capacity utilization
UPS(KVA) x 1000 x Load Power Factor (=1)
Where , DC Current=Inverter efficiency x End Voltage
Hence , VAH = AH x Nominal Voltage
For e.g. : for 3 KVA UPS , 1 hour Backup :
3 x 1000 x 1
DC Current= 17.0 A
0.93 x 10.5 x 18
17.0 x 1.0
Battery ”AH “ = 27.4 AH
0.62
Hence , 18 nos of 12V/28AH batteries will suffice .
TOTAL VAH = 18 x 12 x 28 = 6048 VAH
The following assumptions have been made in the above
calculations :-
1. DC Voltage – 216 for 3 KVA
2. End cell voltage / battery of 10.5 V
3. Load Power Factor = 1.0
4. Inverter efficiency = 93%
% Capacity utilization is :
Duration % Capacity utilization
½ hr (30 mins) 52%
1hrs 62%
2hrs 74%
3hrs 83%
4hr 85%
For ups and invertor battery selection chart lOG On to:-
http://www.sharanapower.com/selection2.htm
| Is This Answer Correct ? | 22 Yes | 10 No |
Post New Answer View All Answers
why tertiary winding is used in transformer with diagram?
What willbe change in programming when we use 5/3 solenoid inplace of 5/2 in operating of a cylinder?
What Is HO factor in power selection
any idea abt REVERSE METERING concept.........?
what is motor capacity of 80TR chiller? and also say what is the formula related temperature, motor capacity, TR?
what is Anti-pumping?
what is doubling factor in making current of a breaker?
why any centrifugal blower draw more current in starting. consider id fan and fd fan?
Best way to measure the Soil resistance of rocky soil, three probe method and four probe method
I completed my BE EEE degree 2006 .... which license should i apply .... ?????
What types of CMOS memories have you designed? What were their size? Speed? Configuration Process technology?
how does this job compare with others you have aplied for?
Name the component u would expect to find in a switchgear assembly?
Dry type transformers
What is purpose of reactor?.What is different between line and bus reactor?