What type of isolation transformer used in UPS's??
It's Star-Delata Or Delata-Star????Why it is used????
Answers were Sorted based on User's Feedback
Answer / sam
its Delta and star only
to provide electrical isolation
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ravi
IT IS DELTA-STAR ONLY.
TO PROVIDE SINGLE PHASE POWER SUPPLY i.e PHASE TO NETURAL
CONNECTION IT IS USED AS A DELTA-STAR TRANSFORMER.
| Is This Answer Correct ? | 11 Yes | 9 No |
Answer / mms
UPS OUTPUT FROM IGBT IS WITHOUT NUETRAL IT IS JUST PHASE
AND CUSTOMER REQUIRED PHASE AND NUTRAL FOR LOAD SO IN UPS
USE STAR OUT PUT TO THE LOAD HENCE THE USE "DELTA STAR"
TRANSFORMER USED IN UPS
FOR EXAMPLE IN SINGLE PHASE UPS OUTPUT(230VAC) WITHOUT
CONNECTING THE DEDICATED EARTH THIS TWO TERMINAL HAS OUTPUT
VOLTAGE FOUND 115 AND 115 VOLTS AND ALSO BOTH POINT TESTER
IS GLOWS THUS WE CONNECT THE EARTHING TO UPS
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / biswajit sahoo
deltastar, beacause neutral is dedicated for ups only. its
neutra is not mixing with raw power neutral
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / hussein
Delta-Star
reason: isolation transformer is to isolate the neutral.
However, the transformer input will be only 3 core cable
(RYB phases) which will be connected as delta, output will
be 4 cores (3 phases and one neutral) and clean earth which
will be commoned to neutral at the star point.
| Is This Answer Correct ? | 1 Yes | 1 No |
in thermal power plant the steam produced is made to cool after falling on the turbine blades. my question is why this is done while the same is needed to heat up again. "jab pani ko wapis garam hi karna hai to thanda kyu karte hai"
Why sometime i receive GCU fault /Excitation voltage loss in my Generator Synch Panel .
What is the purpose of SOTF being used inspite of distance Protection given?
Advantage of 11KV ring main system with open point
1 Answers Alam Group of Companies,
why DC current not used in Transformer action?
17 Answers Engineers India Limited,
what happen if any one phase of a slipring induction rotor winding is open?is it start or won't?
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The slip when motor stalls is A 1 B 0 C 13.33% D 10.33%
why and where we use early make & late break contacts in protection?
What is an automatic controller?
primary of transformer connected to Dc supply in series with switch, and secondary connected on ammeter, what happens when swith On and OFF. (or) if continuously On and OFF
A genarator is connected through a 20MVA ,13.8/138 KV stepdown transformer to a transmission line. at the reciving end of the line a load is supplied through a step down transformer of 10MVA,138/69 KV rating .A 0.72 PU load evaluated on load side transformer ratings as base values ,is supplied from the above system for system base values of 10 MVA and 69 KV in load circuit the value of the load in generator circuit will be ...........
Why the transformer rating is denoted in VA rating why not in KW
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)