if the synchronizing b/w
generator and busbar not
complete and we close the
out going circuit breaker
of generator then what
happen ?
Answers were Sorted based on User's Feedback
Answer / sheikh
if synchronization b/w generator and busbar would not be
completed and if you close the out going CB then generator
have gone to over current tripped or reverse power tripped
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / hamuel vilho
the generator winding wire will become hot and get broken which lead to linkage and it will get damaged,NB it is very expensive to repair winding wire, never try to close the circuit breaker if they are not in the same phases, frequency,
Is This Answer Correct ? | 1 Yes | 0 No |
IF the synchronization does not complete and if you close a cct breaker a severe arcing may occur and generator will trip instantaneously. Because the Generator sides voltages and bus side voltages do not match. To match the volatges following has to satisfied.
1. voltage magnitude
2. phase angle difference - 0
3. phase sequence - same
So at this condition there might be present voltage or phase angles or phase position mismatches. Say for example there exists a voltage magntude mismatch of 1 kV and when you close the cct breaker contact points have that voltage across them and this will cause severe current through contact points of breaker
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kk
First of all check sync relay will not permit to sync due to control ckt configuration, perhaps if it did then gen bkr would tripped in reverse power (32P relay) acted.
Is This Answer Correct ? | 0 Yes | 0 No |
How do you protect your appliances from harm in case of neutral failure in a three phase power supply set up.
Why do we need interlocking in a HT metering or Ring main unit switchgear?
why hv winding is not placed near to transformer core
why the measure taken in multiplication factor of 11for voltage like.. 110V,220V,440V,1.1KV,6.6KV,11KV,33KV,66KV,110KV,132KV,220KV
What is a slack bus?
Is it required to use 2 nos of body earthings to any machine though if we use TP with E supply is provided to Machine?
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.
How does a star connection and delta connection work? How does the star connection save starting current and how does it change to delta?
how to calculate short circuit calculation of the transformer by usuing the percentage impedence? formula needed.
Can any one know what are the symbols at the down (below) the analog ammeter??? there are 4 symbols which are they ?????
How can we calculate the rating of a cable with formula?
Car battery + terminal allways biger than - terminal! Why?