if the synchronizing b/w
generator and busbar not
complete and we close the
out going circuit breaker
of generator then what
happen ?
Answers were Sorted based on User's Feedback
Answer / sheikh
if synchronization b/w generator and busbar would not be
completed and if you close the out going CB then generator
have gone to over current tripped or reverse power tripped
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / hamuel vilho
the generator winding wire will become hot and get broken which lead to linkage and it will get damaged,NB it is very expensive to repair winding wire, never try to close the circuit breaker if they are not in the same phases, frequency,
| Is This Answer Correct ? | 1 Yes | 0 No |
IF the synchronization does not complete and if you close a cct breaker a severe arcing may occur and generator will trip instantaneously. Because the Generator sides voltages and bus side voltages do not match. To match the volatges following has to satisfied.
1. voltage magnitude
2. phase angle difference - 0
3. phase sequence - same
So at this condition there might be present voltage or phase angles or phase position mismatches. Say for example there exists a voltage magntude mismatch of 1 kV and when you close the cct breaker contact points have that voltage across them and this will cause severe current through contact points of breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kk
First of all check sync relay will not permit to sync due to control ckt configuration, perhaps if it did then gen bkr would tripped in reverse power (32P relay) acted.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why arc quenching is used in Diode ?
what are the different type of transformers available in markets???
6 Answers Atomic Energy Commission,
what is the Space heater? why using in Electrical motor?
How impulse levels are calculated that for 11kV impulse is 75kvp, for 24kV impulse is 125kvp ?
Difference between transition and diffusion capacitance
why motor starting current is High ?
testing of transformer
why transformer donot allow the dc?
how system voltage affect the power factor or vice-versa.
how to select a cap,when a fan is required 2.5 micro ferad cap,then how we know about 1 hp motor?
What products have you designed which have entered high volume production?
in which base we defined the conductor is Dog type, Squirrel type, rabbit type, wolf type etc used in transmission line?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)