An 11kv system consisting of an underground cable to a sub
station about 300 meters away was shut down for about 10
hrs. On energising, it tripped off on earth fault about
10---20 mins later 6 times but since than it is not
tripping.its already 3 weeks now. The SPAJ was found to be
fine. what could be the cause.No test had been done to
determine the cause of the trippings till now because of
demand.

Answers were Sorted based on User's Feedback



An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut d..

Answer / k.prakashchandra

If only you had replaced the breaker cubicle and test
charged you would have come to conclusion.If the all 3 poles
do not close almost at the same time and there is a time
gap, the breaker is likely to trip on EFR due to the
unbalanced current in case of 2 OCR + 1 EFR protection
scheme.In such cases it is advisable to test charge on no
load during the second time and confirm the mechanical fault
which is not consistent & does not occur always.

Is This Answer Correct ?    1 Yes 0 No

An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut d..

Answer / pillay

thanks but I had managed to ON the system and remained
energized with some load for a few minutes (10 -20 mins)
before it tripped again on earth fault , it happened 6 times
on (4/6/2011) and till today (13/07/2011) no problem. we
are using ABB spaj oc/ef relay.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Is it acceptable of installing an earth pit in planters area where bare copper cable, earth rod and connection are susceptible to corrosion due to water?

0 Answers  


Impedance relay is directional relay or non directional relay?

2 Answers   KSEB, NTDC,


why substation are rated like 11KV or 33KV?

3 Answers   TNEB Tamil Nadu Electricity Board,


whether the battery is voltage source or current source?

2 Answers  


in india ac frequency is 50hz, but in foreign countries it is 60hz,whwt is the reason

9 Answers   SVIT,






What is the cause for a blown fuse in one phase of primery side(HV) of a three phase transformer( 4169v-460v) in the time of closing its supply breaker. There is no load on the secondery side of the transformer in this moment.

3 Answers   Novachem,


why a three phase induction motor cannot run at synchronous speed ?

7 Answers   RUET,


We have 2 no. 4MW DG set. and GEB supply. But, we running, only 1 DG set. when we done APFC/Power factor setting : 0.90, then winding temp. Low. but when setting done : 0.83, then Winding temp. increase. WHY Why ? ? ?, plz give me answer.

4 Answers  


why we used dc supply for field in dg set

0 Answers   Hindusthan National Glass,


What will happen when more than one star neutral points at same voltage level are connected to earth by metallic conductor?

1 Answers   TCS,


WHAT IS A DIFFERENCE BETWEEN A DC GEAR MOTOR AND STEPPER MOTOR.AND WHICH IS MORE APPROPRIATE TO USE FOR POSITION CONTROL PURPOSE?

1 Answers  


how to calculate no load losses units comsumed by transformer

2 Answers   MRF,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5084)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)