An 11kv system consisting of an underground cable to a sub
station about 300 meters away was shut down for about 10
hrs. On energising, it tripped off on earth fault about
10---20 mins later 6 times but since than it is not
tripping.its already 3 weeks now. The SPAJ was found to be
fine. what could be the cause.No test had been done to
determine the cause of the trippings till now because of
demand.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
If only you had replaced the breaker cubicle and test
charged you would have come to conclusion.If the all 3 poles
do not close almost at the same time and there is a time
gap, the breaker is likely to trip on EFR due to the
unbalanced current in case of 2 OCR + 1 EFR protection
scheme.In such cases it is advisable to test charge on no
load during the second time and confirm the mechanical fault
which is not consistent & does not occur always.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pillay
thanks but I had managed to ON the system and remained
energized with some load for a few minutes (10 -20 mins)
before it tripped again on earth fault , it happened 6 times
on (4/6/2011) and till today (13/07/2011) no problem. we
are using ABB spaj oc/ef relay.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is percentage impedance of transformer? explain its significance
can a 12v dg starting battery(150 AH) be replace by 6 nos of 200AH batteries each of 2v connected in series.
full form of electrical?
Transformer rating=> 15/20 MVA.Why there are two raings? What should be the rating of the fuse at the secondary if the voltage level is 13.8KV/4.16KV?
Why do you have to use Protecion relay with the function MTB ( Mechanical Trip Button ) for electrical system.
In three phase, phase to phase voltage is 440 Volts, but the three phase motors are designed for 415 Volt, 50 hz, why
1 Answers Shree Ram, Shriram, Sri Ram,
What are the different condition monitoring techniques for a motor?
Which of the following are ill suited for energy efficient motors application?
what is the apt definition for kirchoff's current and voltage laws?
What is mean by % impedance of transformer? detail explanations expected.
What are the classification of Servo Motor?
What is the formula to calculate the rating of power cable for three phase current.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)