An 11kv system consisting of an underground cable to a sub
station about 300 meters away was shut down for about 10
hrs. On energising, it tripped off on earth fault about
10---20 mins later 6 times but since than it is not
tripping.its already 3 weeks now. The SPAJ was found to be
fine. what could be the cause.No test had been done to
determine the cause of the trippings till now because of
demand.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
If only you had replaced the breaker cubicle and test
charged you would have come to conclusion.If the all 3 poles
do not close almost at the same time and there is a time
gap, the breaker is likely to trip on EFR due to the
unbalanced current in case of 2 OCR + 1 EFR protection
scheme.In such cases it is advisable to test charge on no
load during the second time and confirm the mechanical fault
which is not consistent & does not occur always.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pillay
thanks but I had managed to ON the system and remained
energized with some load for a few minutes (10 -20 mins)
before it tripped again on earth fault , it happened 6 times
on (4/6/2011) and till today (13/07/2011) no problem. we
are using ABB spaj oc/ef relay.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the significance of tan delta testing?explain the theory?
why master trip(86) used in eletromagnet?
there is a power transformer 66/11kV in delta-delta connection has 5 feeder coming out from the secondary side. One of the feeder in it normally loaded (loaded than other feeder)and this feeder usually trips with double OCR causing the bank transformer to trip. Now if the load of this feeder is put on other transformer then that no problems occurs on that transformer or the load. However normally all the test(IR, PI, short ckt, open ckt,grounding test and other ) has been conducted for this but evertything transformer..... I am not geting what is the actual problem...
can we calculate the diameter of the cable by its cross section?
how we calculate full load current of A.C & D.C Motors?
how the magnetic flux is said to be rotating & alternating?
Enlist four components of electrive drives.
Rccb trip or not with out neutral connect in three phase welding machine
WE HAVE THE DC RECTIFIER 1500A, INPUT VOLTAGE IS 3 PHASE. HOW TO CALICULATE THE LOAD? 3 PHASE SIDE EITHER dC SIDE. PLEASE SUGGEST ME
What does negative slip of an induction motor signify?
Can any one know what are the symbols at the down (below) the analog ammeter??? there are 4 symbols which are they ?????
What will happen if the voltage in my house drops from 220V to any lower voltage?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)