Answer / sobhuza, za
For those who this my answer (Answer 2) is incorrect. It is
important to remember that HT circuit breaker has two
current ratings. One is the continuous current rating. The
other one is the maximum fault breaking rating that the
breaker can carry for about say 2 seconds. The former is
what the question is about. The latter is in kA range
typicaly 25kA or so. Therefore 1250A is just a normal load
current that the circuit breaker can carry.
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / rahul
bcoz CBs are supposed to interrupt fault current which can
be several times larger than the continous load current.
( for further clarification see CB specifications)
Is This Answer Correct ? | 21 Yes | 11 No |
Answer / shan80
there is no necessery to use 1250 vcb for 50A u can use
630A vcb for that load.1250A is only manifaturing capicity
630A vcbs also available and these rating r standard. 1250A
rating is only normal current rating not shot circuit rating
Is This Answer Correct ? | 7 Yes | 5 No |
Answer / vikash kumar
HT breaker is sized based upon the fault current. Here 1250A is the fault current. 50A is the normal current and overload protection is provided by CT and over current relay.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / arjun
it is coz the voltage at the HT side is much high & so is the pressure of the voltage is also much high, therefor the selection of the HT breaker depends on various other factors such as pole distance(distance between the poles of the breaker ) ,voltage (The voltage rating of the circuit breaker must be at least equal to the circuit voltage.), ambient temperature,overload,continuous current rating & max current it can handle before tripping .so even if the current though a HT circuit is low we need a breaker of much higher ratting
Is This Answer Correct ? | 3 Yes | 5 No |
Answer / v.v.j.rao
The rating of the breaker current 1250 means it can carry
1250 amps after that % over loaad depends on O/Load setting
of 50%,75% or 100% only.If you put this breaker at 50 amps
oad this will not trip under any O/L condition of that
particular load.
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / sobhuza, za
It's because the equipment is rated based on the capacity
levels and not at loading levels. CB ratings are
standardised, as it may happen that the loading on one
circuit is 50A, but on another it can be 900A. So for
rating purposes it is better to standardise at say 1250A so
for ease of procurement. Remember that when the load
increases over time and you won't have to change CBs due to
loading increase.
Is This Answer Correct ? | 11 Yes | 16 No |
Answer / sbb
It is because we cannot measure the high current directly.So
for this we will keep CT's to measure high currents.In
primary side it will be 1250A and in secondary side it will
be 50A,this is nothing but CT Ratio.
Is This Answer Correct ? | 1 Yes | 16 No |
What is the maximum No. of out going mccbs permitted from an LV distribution paqnel? What is the ampere relation between incomer and out going switch gears/mccbs?
HI....HOW CAN BE MESARED THE VALVE OF NEUTRAL GROUND RESISTOR WHIC IS LOCATED AT SWICHGEAR ON GENERATOR SIDE....
whatis the commertial spec. of distribution boards ?
what is the burdon in case of relays?
1 KW = how many kva
Which Kind of machines(in terms of poles) give the smoothest DC
what are pilot cells
Why do we choose 33kV transmission for industrial purpose and 11Kv for township?
in case of three phase induction motor,when it is connected to three phase supply,why the magnetic field is rotets around the armeture?
what is the difference between relay, contactor
4 Answers BRSS, Vishay Intertechnology,
What is the general power consumption rating of CPU CRT type and Flat type, Monitor,Printer, projector, Scanner?
What is the minimum load that you can keep in a 3 Phase 40 KVA Diesel Generator? Is it neccessary to load all the 3 phases? Can a phase be left without load?