Answer / gunasekaran
protection ct is operating below the knee point voltage but
metering ct is operating almost saturation point.accuracy is
more in metering ct accuracy is not important under normal
condition. metering ct accuracy is 25%to 120% of the rated
current but protection ct is not like that suppose the ct
5P10 and 20VA burden 10times current in primary 5% error is
acceptable up to 10 times current it will feed 20VA burden
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / d.lakshmi narayana
The difference of protection ct & measuring ct is the
protection ct secondary current is very accuracy .Ex 600/1A
ct is the sec current is Exactly coming 1A But metering ct
is not accuracy That same ct is coming Sec current is
0.98--0.97 A
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / ahir ashish
protection ct is depand upon the ratio error and measureing
ct is depand upon phase angle error.
| Is This Answer Correct ? | 2 Yes | 4 No |
at work i have a genertor/alternater what is the easyest way to work out if it is dc or ac?
we use capister for power factor. when we use capaciter in dg circuit than defect dg. can we use capaciter bank for dg circuit
How to calcute the cable size for both HT and LT please specify the formula for that Regards Chethan C
Need help. 3 phase system. Neutral line arced and melted upon connection of connector with 3 phase power. Why would that happen?
what is mean by lookup table in microprosser.
Why we are designed only 11Kv and 6.6Kv Alternators, not 33Kv Alternators and Power Transmission side we are designed only 220kv, 120kv, 66kv, 33kv, 11kv, and 440volts, not 20kv, 50kv, 100kv.
Wat is meant by OLTC?
what is the power factor used by the PHCN in nigeria? 2. what is the difference between an alternator and generator. 3. Generation of poweris in KV but how is transmission is in MW. 4.If the transmission of power is 20,000MW how can it be increaesed to 80,000MW
Can we use same copper cable for both AC & DC power.
In power point wiring,often,we use less size of earth wire compared to phase & neutral wire and we use big size pin in pug top. how is it justified? can we use small size cable for earthing?
define electrical field?
how calculate external illumintion in a compound area. for e.g. there is one open park having 600m2 area and i have to put 40w flouresent tube fitting with pole. how shall i calculate the numbers of fitting.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)