Answer / gunasekaran
protection ct is operating below the knee point voltage but
metering ct is operating almost saturation point.accuracy is
more in metering ct accuracy is not important under normal
condition. metering ct accuracy is 25%to 120% of the rated
current but protection ct is not like that suppose the ct
5P10 and 20VA burden 10times current in primary 5% error is
acceptable up to 10 times current it will feed 20VA burden
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / d.lakshmi narayana
The difference of protection ct & measuring ct is the
protection ct secondary current is very accuracy .Ex 600/1A
ct is the sec current is Exactly coming 1A But metering ct
is not accuracy That same ct is coming Sec current is
0.98--0.97 A
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / ahir ashish
protection ct is depand upon the ratio error and measureing
ct is depand upon phase angle error.
| Is This Answer Correct ? | 2 Yes | 4 No |
is it possible to export & import power in a same transformer.how
why DC motor body is plain cover but AC motor is different like finse?
What are the technical reasons for soaking transformers for various times before allowing them to pick load after a fault ?
after syncnhronistion how generator speed controlled by grid
Whai isPCC and MCC Difference?
What are the effects of adding a zero to a system?
In hydel power plants, L.A's, S.C's are placed inside the control panel boards. what is the purpose? [already the total body was earthed to ground.]
ct connection of energy meter
What is difference between unity power factor wattmeter and upper power factor wattmeter? In short circuit test of transformer the wattmeter used is unity power factor type or upper power factor type wattmeter?
0 Answers Jindal Steel and Power,
Befor synchronissation of Generator what test to be carried out.pl.specify with reason.
I have a shop heater with a 1/3 hp capacitor start, induction motor driving the fan. Intermittently, the fan motor speeds up significantly for several seconds (15-60 sec) then slows to normal operating speed. The manufacturer suggested changing the capacitor which made no sense, but I did it to no avail. Could this possibly be caused by the centrifugal switch intermittently reconnecting the start winding?
what is mean by unity power factor?why are u calling Resistivity load also unity power factor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)