Answer / kanchan dogra

Selection of HT cable is based on
1. short circuit calculation
2. Full load current capacity
1. Short Ckt. calculation
if total load is 3000 KVA, V 11 KV
short ckt MVA on HV side = 350 MVA (As per standard practice)
short ckt. current Ik= MVA/root3 x KV
350/root3 x 1= 18.4 KA
duration of short Ckt= 1 Second
cross section area of the conductor = Ik x root T/.094
18.4x root T/.094 = 95 SQ.mm

2. Full Load current
Total Load= 3000 KVA
System Voltage= 11 KV
Full load current = KVA/ root3 x KV
3000/root 3 x 11= 157 Amp.
derating factor = .7
current carrying capacity after derating = 157/.7 = 224.95 AMP.
Hence select cable for this current.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

how can i get an electrical c-certificate?

0 Answers   Wartsila,


why ht cable end termination don't have a gland?

0 Answers   Private,


Why is transformer core is earthed

3 Answers  


A resistance, inductance & capacitance are connected in series between points A & B.The voltage drops across the resistance,inductance&capacitance are found to be 40V,70V&100V respectively. What is the total voltage between between points A&B (Vab)? a)210V b)70V c)50V d)230V

6 Answers  


How current is reduced in STAR connection?

6 Answers  






What is the difference between earth and neutral

4 Answers   ABB, Tamboli Engineers,


why we multiply 11 in High Electric supply?(eg.11KV, 33Kv, 330Kv etc.)

3 Answers  


over frequency is the protection of turbine or alternator?

2 Answers  


In cable sizing calculation (determining the max route length of cable) why we choose the shortest length between cable length of full load current Iflc & starting current Istart?

0 Answers  


Why is better to have a minimum ceiling voltage of 250% than 160%?

0 Answers  


why on axial hitting up of air blast on hydrogen produced in oil circuit breaker,temperature rises of the core of the arc?

0 Answers  


ASTM D 3455 - Standard Test Methods for Compatibility of Construction Material with Electrical Insulating Oil of Petroleum Origin has been used for Testing Transformer Oils with a product placed in it. Aged Control Oil has a Power Factor of 0.032% at 100°C. Aged Oil with a Test component has a Power Factor of 0.093% at 100°. Is this increase acceptable? If not why? How much increase is acceptable?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)