How to calcute the cable size for both HT and LT please
specify the formula for that
Regards
Chethan C
Answer / kanchan dogra
Selection of HT cable is based on
1. short circuit calculation
2. Full load current capacity
1. Short Ckt. calculation
if total load is 3000 KVA, V 11 KV
short ckt MVA on HV side = 350 MVA (As per standard practice)
short ckt. current Ik= MVA/root3 x KV
350/root3 x 1= 18.4 KA
duration of short Ckt= 1 Second
cross section area of the conductor = Ik x root T/.094
18.4x root T/.094 = 95 SQ.mm
2. Full Load current
Total Load= 3000 KVA
System Voltage= 11 KV
Full load current = KVA/ root3 x KV
3000/root 3 x 11= 157 Amp.
derating factor = .7
current carrying capacity after derating = 157/.7 = 224.95 AMP.
Hence select cable for this current.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why open circuit test of transformers is conducted at rated voltage??Why not any other voltage??
What is the difference between earthing & neutral.
At what load maximum effiecency will be obtained Distribution transformer and Genarating transformer Pls clarify?
why middle phase should used for earth fault and other phases used for over current in overcurrent and earth fault relay?
How to convert KV into MV in a Transformer?. dont say multification of 1000.pls give practical convertion factor.
How much width of the land shall have to be left below the EHT line of 440 kv as per the rule. i am told that a corridor of 35 M width is to be left free below 220 kv line. please confirm
Has someone here done a sizing for a generator (3 phase), its for a pumping station. If you have an example for standby/duty and both running (I) star delta (ii) Soft Starter.
in house wiring when two wires are same colour coding and there is no any connection one end how to find which wire is earthing wire
Which starter can be used for 3 phase verriable speed (2 stator wdg) induction motor ?
How much duration I can keep open the CT if it is under loading condition(100 Amp load)?
3 Answers Infosys, NTPC, Suzlon,
Difference between EDO and MDO breakers?
How to take vector group test for Ynd11 transformer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)