In power point wiring,often,we use less size of earth wire
compared to phase & neutral wire and we use big size pin in
pug top. how is it justified? can we use small size cable
for earthing?
Answers were Sorted based on User's Feedback
Answer / santosh kawade
We use big size pin and socket for power point to reduce
resistance in earth pat and to alway connect earthing first
to equipment before connecting mains and neutal in system.
Using low size cable for earthing in single phase can not
be justified, we have to use same size cable for neutral,
eathing and mains.
In three phase we can use lower size cable for earthing and
neutral.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / j@ru ( sati)
as we know from R =pl\A bigger the size of area lesser the
resistance of conductor...so b using this concept earth pin
provides less resistance to leakage current compared to
other two pin hence leakage current by pass to earth without
damagng appliances..
thats all thank you
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / shanmugam annamalai
The reason of earth point in bigger than that others to
save the equipments from leakage current. It means, the
system will be earthed before connecting to the power
supply. Ultimately, if there is any leakage current, it
would bypassed through earth so equipment will be safe.
Please reply, It you need more clarifications
| Is This Answer Correct ? | 4 Yes | 2 No |
What happens when DC supply is given to transformer
how to reduce the transformer size in ups ?
some times voltage does not built in small generators why ?
why the transformer connected like STAR- STAR, DELTA- DELTA, STAR- DELTA, DELTA-STAR ...? why these connections ,,, explain the advantages these connections?
What does “battery of 180 AMP HOUR” mean to you?
What should be the minimum and maximum ohmic value for earthing?
Why short ckt does not happen when solenoid coil connected to supply. as its a wire only.
Hello sir, pls send me hpcl technical test papers .i am. Appearing for the exam.
why nutral and earthing wire connect with each other in main panel board.
what is difference between 2 pole structure and 4 pole structure in transformer yard
Dear Mr B C pal...Can you plz. put some light on principle of operation of Z-Ct in conjunction to its use with 1Cx1000Sqmm HT Cables & Directional Ground Fault / Over Voltage Relays...Regd..Parag v K 9899115632
if d gen is 50kw,load is 60 kw,hw d gen ll supply d remaining power?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)