How to check the SCAN time of DCS ,n dont give therotical
answers .How to check the SCAN time of DCS during FAT?
Answers were Sorted based on User's Feedback
Answer / rajkumar
If you are using a DCS (Distributed Control System), there
should be a diagnostic utility that you can run (this is
usually part of the system software). If your sotware scan
is structured correctly i.e. all software is called in
cyclic scans and not free scans, the utility should be able
to tell you the loading of these scan cycles.
You should also be aware that you are doing this under FAT
conditions. This would imply that most of your IO are not
connected, which in turn would push up your scan times for
all the diagnostic alarms comming in.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / rnm
In my opnoin, Sacn time checking during FAT shall be input
simulation with one repeater block. Then go for cycle sacn
rate check, which will cover input,process block(PID) and
output. We know, there wiil be no O/P connected in field
and no much execution of loops. In this case, very
difficult to conclude this time.Better to check I/O
scanning rate.
Is This Answer Correct ? | 0 Yes | 0 No |
What are the processes Variables?
How to Calibrate Transducers? Can you give me a step by ste procedure?
how we can measure the interface level?is it possible to measure interface level with dp or pressure transmitter?
What is the detail function of I/O card in DCS ? Why we dont use the I/O directly with controller?
why pressure 3-15psi is used as industrial standard and what is the reason
2 Answers JAL International, UltraTech,
WHAT IS D/O D/I AND A/O A/I PLZ EXPLAIN
What is the Flow rate ?
What are the application of bernoulli’s theorem?
it is possible to check the fail safe condition in pressure transmitter. if possible how?
what is the difference between Feedback controller and Feed forward controller. and when it is to be used.
During valve sizing from all calculation you got flow coefficient CV 12,than what it means? like for selecting pressure transmitter if your MAWP is 12 bar than you select a capsule of max. 20 bar which cover your mawp 12 in same way for selecting control valve If CV is 12 than how we use it in selecting valve??????
Explain level troll principle & interface level measurement.