How to check the SCAN time of DCS ,n dont give therotical
answers .How to check the SCAN time of DCS during FAT?
Answers were Sorted based on User's Feedback
Answer / rajkumar
If you are using a DCS (Distributed Control System), there
should be a diagnostic utility that you can run (this is
usually part of the system software). If your sotware scan
is structured correctly i.e. all software is called in
cyclic scans and not free scans, the utility should be able
to tell you the loading of these scan cycles.
You should also be aware that you are doing this under FAT
conditions. This would imply that most of your IO are not
connected, which in turn would push up your scan times for
all the diagnostic alarms comming in.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / rnm
In my opnoin, Sacn time checking during FAT shall be input
simulation with one repeater block. Then go for cycle sacn
rate check, which will cover input,process block(PID) and
output. We know, there wiil be no O/P connected in field
and no much execution of loops. In this case, very
difficult to conclude this time.Better to check I/O
scanning rate.
| Is This Answer Correct ? | 0 Yes | 0 No |
how we will install a positioner ?
how to tune siemens sipart electro pneumatic positioner..plz tel me..
can i get any detail of interview question asked for instrumentation,plc,scada ,dcs..............
I want to measure level under vaccum by using DP Tx and vaccum vary between -500 to -670 mmHg and process fluid is accetic anhydride if consider process fluid density 1 kg/cm2. how to calibrate Tx ? consider level is 0 to 100 Cm.
State bernoulli’s application.
how checking is done in fiber optic cable? explain the working of RTU?
flow transmitter formula?
1 Answers BEMCO, Siemens, Yokogawa,
What is stripper & spilitter ? Diffrence in this.?
how to overhaul control valves.what are the proper procedures.
What are the logic behind 2x2 and 2x3 logic and more when ask in interviews
please suggest me, how can i change the display setting in term of unit in place of % of Honeywell pressure transmitter ST3000S100?
During valve sizing from all calculation you got flow coefficient CV 12,than what it means? like for selecting pressure transmitter if your MAWP is 12 bar than you select a capsule of max. 20 bar which cover your mawp 12 in same way for selecting control valve If CV is 12 than how we use it in selecting valve??????
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)