How to check the SCAN time of DCS ,n dont give therotical
answers .How to check the SCAN time of DCS during FAT?
Answers were Sorted based on User's Feedback
Answer / rajkumar
If you are using a DCS (Distributed Control System), there
should be a diagnostic utility that you can run (this is
usually part of the system software). If your sotware scan
is structured correctly i.e. all software is called in
cyclic scans and not free scans, the utility should be able
to tell you the loading of these scan cycles.
You should also be aware that you are doing this under FAT
conditions. This would imply that most of your IO are not
connected, which in turn would push up your scan times for
all the diagnostic alarms comming in.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / rnm
In my opnoin, Sacn time checking during FAT shall be input
simulation with one repeater block. Then go for cycle sacn
rate check, which will cover input,process block(PID) and
output. We know, there wiil be no O/P connected in field
and no much execution of loops. In this case, very
difficult to conclude this time.Better to check I/O
scanning rate.
| Is This Answer Correct ? | 0 Yes | 0 No |
when the force applied on load cell the ohms will be varriying .and how its convert ohms to mv generate and have any formulae?
1 Answers UETCL Uganda Electricity Transmission Company Limited,
difference between transducer and converter in instrumentation
what is the difference between active & reactive power?
What is standard of DCS panel design?and what is step of DCS panel design?wiring and type of connector(screw or DB connector)
What is the difference bitween control net scaner and device net scaner
draw a loop drawing of vibration beginning to end
WHAT IS SELF CLEAN ELCTRODE IN MAGNETIC FLOWMETER?? WHAT DO YOU MEAN BY THIS TERM??
Tell me about PID Tuning and what is PID.
How can we use feedback signal frm rtd for monitoring and in dcs for controlling ,then which type of rtd is sutaible 2 , 3,4wire and why ?
In control valve proximity inductive sensor is taken as digital feedback for full open and full close.Normally its volts 24v when the sensor acts the feed back voltage 14v so that our relay not indicating in plc panel . kindly give the solution.
Dear All can any one told me that VFD Make ABB Model ACS800-01 used for dual Source like 1.DC Source applied at terminal UDC+,UDC- 2. 3 phase 400AC,50Hz
what is instrument philosophy
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)