why the motor running in delta connection ? it can be in star?
Answers were Sorted based on User's Feedback
Answer / shahulsnfa
all the above is not seems to be correct.. the real thing
is in star IL=Ip so we are going for star at the time of
starting. after the machine attains rated speed we are
changing into delta becuase the machine cannot develop
rated TORQUE of the motor in star but it can develop in
delta since in delta VL=VP. that's why its changed to delta
instead of running in star. V is directly proportional to
flux is inturn proportional to torque.
| Is This Answer Correct ? | 78 Yes | 9 No |
Answer / madhav agrwal
When a delta motor is connected in star, the voltage across
the windings is reduced by the square root of three
resulting in reduced flux in the iron, this will reduce the
magnetizing current, and will also reduce the torque
capacity of the motor
| Is This Answer Correct ? | 40 Yes | 3 No |
Because the voltage in star connection is Vph=VL/square
root of three.
But in delta connection Vph=VL.
So in star connection is only for starting a motor.
But to run a motor through a delta winding. Becaus then
only full voltage given to motor and it will run in full
speed.
| Is This Answer Correct ? | 55 Yes | 26 No |
Answer / rajendran
The type of connection in which the motor is running
continiously depends upon its design and the type of
application it is used...
there are motors designed for continious star opearation...
But the basic thing is star is preferred for starting and
delta is preferred for runnnig owing to design as well as
economic feasibilities...
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / maged
Simple 3 phase motors can be connected in either STAR or
DELTA.
In star the maximum power is reduced but the starting
current is lower than for Delta
In Delta the motor gives maximum power but the starting
current is often too high and the overload trips out.
To overcome this a star/delta starter is fitted
All 6 wires from the motor windings are connected to the
starter and the starter functions are as follows :-
When start button is pressed the motor is automatically
connected in star and the start current is acceptable. At
the same time a timer is initiated and after a
predetermined time the starter automatically changes from
star connection to delta. The motor now runs in Delta until
switched off.
This is a fully automatic starter, many years ago manual
changeover star/delta starters were more common.
| Is This Answer Correct ? | 20 Yes | 6 No |
Answer / shaji samuel
Motor can be connected in delta as well as star.
In delta connection the maximum power that motor can give
is motor rating.ex 15 kw motor 15kw power.
In star connection the maximum power motor can give is
(motor KW * 1/3). Now the motor is derated.
Also note that if your motor 50% only loaded then the motor
winding can be connected in star instead of delta. This
will give you power saving. Also take care that always load
on motor is less than 50% or else motor winding will get
burnt. For more clarification mail me on
shajisame@gmail.com
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / ramasamy
Motor running with star or delta depends upon the design,the same is given in the name plate.The reason for most of the motors are in delta is to limit the starting current by turn ON in star connection & than converting to delta connection to get the rated speed & torque. Where as it is not possible if the motor design is star. But now we get more of star connection design motor which are VFD & soft starter application.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / samir vyas
Its a matter of torque which is low in star because of reduced voltage at
winding and at designed load star connected motor get stopped due to
insufficient torque. More you have to see motor characteristic at diff.
Stage
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dhanu
speed is depends on frequency and no. of poles.
| Is This Answer Correct ? | 28 Yes | 31 No |
Answer / a.venkatswami
motor running in delta it can be in star beacuse star
connected motor has taken voltage root three times and
current high that the cost is high threrfore motor runngin
in delta but in industres star motor connection also
working its motor rating low kw.
| Is This Answer Correct ? | 4 Yes | 8 No |
what happen if turbine trip ,g.c.b not open and excitation on condition?
A Question Like A Wire Is Wound Whose Resistance Is Some 132. 44647 Ohms. If A Voltage Of 30 mv, 296 Ma Current Is Applied To It What Is The Resistance.
what is kvarh? Please difine it With calculation
To test Transformer we give HT side 440V to see wheather that it is producing 17.6V on LT to verify Voltage ratio is correct or not but when we give the 440V voltage to LT side then what will happen to HT voltage ?
What are all the conditions to protect generator & turbine in thermal power plant?
1 Ton is equal to how many watts?
transformer core are laminated for what purpose?
what will happen if synchronous machine rotor fed from single phase ac supply
what is the difference between NC & CNC machine.what is the difference between equipment & machine tool
What is formula calculation size cable wire ?
State the other types of Air Conditioners?
How to calculate cable rating for 3 phase supply?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)