why the motor running in delta connection ? it can be in star?
Answers were Sorted based on User's Feedback
Answer / shahulsnfa
all the above is not seems to be correct.. the real thing
is in star IL=Ip so we are going for star at the time of
starting. after the machine attains rated speed we are
changing into delta becuase the machine cannot develop
rated TORQUE of the motor in star but it can develop in
delta since in delta VL=VP. that's why its changed to delta
instead of running in star. V is directly proportional to
flux is inturn proportional to torque.
Is This Answer Correct ? | 78 Yes | 9 No |
Answer / madhav agrwal
When a delta motor is connected in star, the voltage across
the windings is reduced by the square root of three
resulting in reduced flux in the iron, this will reduce the
magnetizing current, and will also reduce the torque
capacity of the motor
Is This Answer Correct ? | 40 Yes | 3 No |
Because the voltage in star connection is Vph=VL/square
root of three.
But in delta connection Vph=VL.
So in star connection is only for starting a motor.
But to run a motor through a delta winding. Becaus then
only full voltage given to motor and it will run in full
speed.
Is This Answer Correct ? | 55 Yes | 26 No |
Answer / rajendran
The type of connection in which the motor is running
continiously depends upon its design and the type of
application it is used...
there are motors designed for continious star opearation...
But the basic thing is star is preferred for starting and
delta is preferred for runnnig owing to design as well as
economic feasibilities...
Is This Answer Correct ? | 20 Yes | 5 No |
Answer / maged
Simple 3 phase motors can be connected in either STAR or
DELTA.
In star the maximum power is reduced but the starting
current is lower than for Delta
In Delta the motor gives maximum power but the starting
current is often too high and the overload trips out.
To overcome this a star/delta starter is fitted
All 6 wires from the motor windings are connected to the
starter and the starter functions are as follows :-
When start button is pressed the motor is automatically
connected in star and the start current is acceptable. At
the same time a timer is initiated and after a
predetermined time the starter automatically changes from
star connection to delta. The motor now runs in Delta until
switched off.
This is a fully automatic starter, many years ago manual
changeover star/delta starters were more common.
Is This Answer Correct ? | 20 Yes | 6 No |
Answer / shaji samuel
Motor can be connected in delta as well as star.
In delta connection the maximum power that motor can give
is motor rating.ex 15 kw motor 15kw power.
In star connection the maximum power motor can give is
(motor KW * 1/3). Now the motor is derated.
Also note that if your motor 50% only loaded then the motor
winding can be connected in star instead of delta. This
will give you power saving. Also take care that always load
on motor is less than 50% or else motor winding will get
burnt. For more clarification mail me on
shajisame@gmail.com
Is This Answer Correct ? | 8 Yes | 2 No |
Answer / ramasamy
Motor running with star or delta depends upon the design,the same is given in the name plate.The reason for most of the motors are in delta is to limit the starting current by turn ON in star connection & than converting to delta connection to get the rated speed & torque. Where as it is not possible if the motor design is star. But now we get more of star connection design motor which are VFD & soft starter application.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / samir vyas
Its a matter of torque which is low in star because of reduced voltage at
winding and at designed load star connected motor get stopped due to
insufficient torque. More you have to see motor characteristic at diff.
Stage
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / dhanu
speed is depends on frequency and no. of poles.
Is This Answer Correct ? | 28 Yes | 31 No |
Answer / a.venkatswami
motor running in delta it can be in star beacuse star
connected motor has taken voltage root three times and
current high that the cost is high threrfore motor runngin
in delta but in industres star motor connection also
working its motor rating low kw.
Is This Answer Correct ? | 4 Yes | 8 No |
How to perform a DC resistance test In Alternator and their proceduces?
formula for incomer breaker size calculation of powerfactor correction unit
What exactly is meant by harmonics and harmonic current?? and what is skewing with regard to this??
What is the meaning of Insulation H for transformers????
What is gain margin?
Define the overload capacity of the motor?
how many joints are allowed in underground HT cable of 1 KM
how can get electrical c licence.now i am working in spining mill , transformer capacity 2750KVA. SANCTION DEMAND 2250KVA. PLEASE ADVISE ME . MY CONTACT NO 09944226823
sir, What is the purpose in Generating power plant is operated Lagging PF and Above 0.9 lag PF?
how "rabbit ACSR" conductors are more efficient than "weasel ACSR" conductors
whats is the role of power factor in designing a tariff structure?
how do we connect mcb in our home?and how does it work?