What is surger vector in 33Kv transmission feeder? We have
AC power generator of 8MW which is paralleled with 33Kv EB
grid. Some times our HT breaker gets trip off due to surge
vector problem. How to over come it? Is there any device to
observe the surge and avoid tripping?
Answers were Sorted based on User's Feedback
Answer / rajendran
I think the question is about the vector surges in the
transmission lines....
These surges are sharp dips in the quantity of the
transmission lines happening due to the severe loading or
faults in the transmission lines...
usually when the generators are connected in parrellel
with the grid it will be provideed with the VSR protection
inorder to avoid the overlaoding of the generator during
the micro second grid failures (during the vectro surge)...
We can not eliminate the inherent surges in the
transmission lines....
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / senthil
this phenomena is called as vector surge, for examole line
is closed with out checking synchrnous , so due to
unbalance disturbance may happen, this can be sensed by
fixing vector surge relay
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / prem
you can use an M#3 relay for vector surge protection....
it is quiet useful and a little bit problamatis in programming
Is This Answer Correct ? | 0 Yes | 0 No |
1.what is bus cuplour and main funtions. 2.what is main function of alternator. 3.how many types of dg oils.
I COMPLITED MY B.TECH AND 10TH CLASS WITH 70%MARKS BUT 12TH CLASS 55%MARKS..CAN I GET INDIAN RAILWAY RECUREMENT EXAMINATION?
How can you sized or estimate the ligthning arrester current rating?
Does increase or decrease of reactive load affects the Voltage.
which motor is used in watch..??????
How can we calculate the rating of capacitor bank to be connected for a particular load(ex.100kw)to improve the power factor from 0.8 to 0.9?
In Aeroplane what circuitry or method use for earthing?
9 Answers Bhel, EDA, Wind World,
what is the generator rating for 40 amp load of 3phase motor.?? 400v voltage of generator... plz tell me with formula its urgent...plzzz... and also tell me that this 40 amp at all phases mean 40 amp on red,40 amp on yellow,40 amp on blue...... or the total sum of that 3phase is 40 amp....
What is the difference between phase, neutral wire and earth cable. if neutral is connected to ground, y we need earthing cable? what difference in hot and cold wire? do neutral wire carry current?
What is the fundamental cause of transients in power system?
For 7.5kw star delta starter how to calculate 1. Mccb rating 2. Contactor rating 3. Over load relay rating
what are the major difference between 3phase 3wire and 3phase 4wire trivector meter?