Answer / rajendran
I think the question is about the vector surges in the
transmission lines....
These surges are sharp dips in the quantity of the
transmission lines happening due to the severe loading or
faults in the transmission lines...
usually when the generators are connected in parrellel
with the grid it will be provideed with the VSR protection
inorder to avoid the overlaoding of the generator during
the micro second grid failures (during the vectro surge)...
We can not eliminate the inherent surges in the
transmission lines....
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / senthil
this phenomena is called as vector surge, for examole line
is closed with out checking synchrnous , so due to
unbalance disturbance may happen, this can be sensed by
fixing vector surge relay
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / prem
you can use an M#3 relay for vector surge protection....
it is quiet useful and a little bit problamatis in programming
| Is This Answer Correct ? | 0 Yes | 0 No |
what is upper impedance and lower impedance of a distance relay
WHAT IS START TO INDUCTION MOTER IN STAR TO DELTA OF >5HP ?
Difference between on line capacitor and Station type capacitor.
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
1 Answers Bhel, Indorama, Power Grid,
why a fan starts rotating in the reverse direction when condenser gets damaged?
what time should we set to come on star contacter in stardelta starter?and for what reason we hav to set such time delay range?
1. what type of winding of slip ring ac induction motor rotor and why. 2. how the heating element use in two phase (415 volt)and what rating of element, you prefered.
What should be distance required in between two phase of HT cionductors in open area??????
Difference between ELCB and RCCB?
power generation unit kw/hr or kw/day ?? please answer me engr_kalam@yahoo.com
What is the full form of PSD & CSD ?
6 Answers NIFT, PNG Power, PSD,
What is the inside of ACB & VCB & SF6 breaker's pls tell me about this
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)