Difference between ELCB and RCCB?
Answers were Sorted based on User's Feedback
Answer / guest
ELCB is basically voltage operated tripping mechanism.When a
voltage exists between the earth and frame the tripping coil
is activated.If the earth connection is bad the tripping coil
will not operate.
RCCB is an improvement of the voltage operated tripping
mechanism.This is current operated. If the leakage current is
of the designed minimum amount the tripping mechanism is
activated.So if the earthing connection to the ground is bad
but the leakage occurred through a person to the ground the
RCCB will still trip.
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / prabhu
elcb means-earth leakage circuit breaker
rccb-residual current circuit breaker
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / simon
elcb means-Earth Leakage Circuit Breaker
rccb-Residual Current Circuit Breaker
BOTH R TWO FACES OF A COIN.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / omprakash sahu
Elcb is working based on Earth leakage current. But Rccb is
not having sensing or connectivity of Earth, because
fundamentally Phase current is equal to the neutral current
in single phase. That’s why RCCB can trip when the both
currents are deferent and it withstand up to both the
currents are same. Both the neutral and phase currents are
different that means current is flowing through the Earth.
Finally both are working for same, but the thing is
connectivity is difference.
Is This Answer Correct ? | 2 Yes | 5 No |
WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?
13 Answers Tech Mahindra, Technip,
how we could know that generator running anti clockwise with seeing the rotating direction of prime mover or engine
what is the use of the puls transformer in UPS & how it works???????????
why capacitor burst?
WHAT INSTRUMENT IS USED TO MEASURE THE MAGNETIC FLUX?
what is v/f control in VFD?
what is the current rating of 2500 KVA,33KV/433v transformer on secondary(LT) side
9 Answers Reddy Labs, Vitrum Glass,
What should be the overcurrent, instantaneous overcurrent, short cicuit current settings (i.e. how many times of motor full load and what is the time duration) for a motor?
What should be the BDV value of a new transformer oil
HOW WE CALCULATE CURRENT IF THERE ARE NOT PRESENT ANY AMMETER OR MULTIMMETER??????
Please clarify, 1. Is it required to lay two runs of GI wire along with Armoured LT cable if it is laid between one big mains (63Amps TPN SDF) to small main (32A TPN SDF) with proper glanding termination? 2. If the armoured cable with proper glanding is laid from DB to CNC machine, is it required to run two runs of body earthing to the Machine from DB? 3.If the armoured cable with proper glanding is laid from Substation to Hangar, distance is approx. 100 mtrs, is it required to do earthing at shop area though the primary termination at substation is earthed through gland.
what is the difference b/w absolute encoder and incremental encoder?