Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


if we use fuse in neutral what will happen?

Answers were Sorted based on User's Feedback



if we use fuse in neutral what will happen?..

Answer / silamparasan p.

Fuse is used to limit overcurrent. So we have to use fuse
in phase only.

Neutal is for pass, if any faulty current or unbalanced
current. We dont know how much Ampere current flows through
the neutral during any fault or unbalance, it may be high
current also. If we use fuse in neutral during faulty
current the fuse in neutral will blown and it will camage
the unbalanced power system. And it will damage yje
components.

Is This Answer Correct ?    33 Yes 3 No

if we use fuse in neutral what will happen?..

Answer / s.samjeba singh

Fuses are used to protect the equipment connected in the
circuit to protect from over current. phase is the entry
path for supply and neutral is the return path of suppy if
we use the fuse in return path(neutral) the equipment
connected in the circuit will get damage then only the
supply will reach the fuse

Is This Answer Correct ?    6 Yes 3 No

if we use fuse in neutral what will happen?..

Answer / saurabh chaubal

Firstly by electrical electricity board it is said so and if
we put fuse in neutral then if bcoz of over current the fuse
will blow out in neutral. But the person who is touchin the
live conductor will get a shock.... As there is no
protection there...

Is This Answer Correct ?    7 Yes 6 No

if we use fuse in neutral what will happen?..

Answer / pattabiraman

if this is an unbalance three phase system with single phase loads, Neutral is what locking the phase only, to single phase loads.
When neutral get open, the single phase loads in the system get connected between phases by serial connection. if the load are equal by chance, the loads will still work safely
if loads are unequal, smaller loads tend to get more voltage and larger loads will get lower voltage, leading to burning of smaller loads.

Is This Answer Correct ?    1 Yes 0 No

if we use fuse in neutral what will happen?..

Answer / k.prakashchandra

Additionally , if neutral fuse blows off , all single phase appliances are affected

Is This Answer Correct ?    1 Yes 0 No

if we use fuse in neutral what will happen?..

Answer / cyber4india

The neutral should be solid and only Link should be provided
in neutral as if fuse is provided, in case of shock, it will
blow due to overload, but the supply will be available
through phase and the purpose of fuse is defeated.
In some case(domestic wiring) the neutral also contains
some potential due to unbalance of load in the supply (3
Phase). This holds true even if you are using the one out of
three phase . The neutral is displaced due to uneven
loading. Hence for any purpose of working, neutral Links
should also be disconnected along with the fuse in phase supply.

Is This Answer Correct ?    2 Yes 2 No

if we use fuse in neutral what will happen?..

Answer / arunodayam

Neutal is for pass, if any faulty current or unbalanced
current. We dont know how much Ampere current flows through
the neutral during any fault or unbalance, it may be high
current also. If we use fuse in neutral during faulty
current the fuse in neutral will blown and it will camage
the unbalanced power system. And it will damage

Is This Answer Correct ?    0 Yes 0 No

if we use fuse in neutral what will happen?..

Answer / valentine

in case of a fault and a fuse put in neutral the fuse will not blows out the person in contact with the live part will continue to get a shock which will deny the purpose of fuse, the fuse will trip only in case of over current

Is This Answer Correct ?    1 Yes 2 No

if we use fuse in neutral what will happen?..

Answer / gobinath npt

neutral is return path.. the electrons flow is only in phase..
so only the phase control is given to switch..if we provide
fuse in neutral its not safety for the equipments connected in
circuit when the current exceeds the limit...i.e... over
current..

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

If the kvar rating of capacitor bank is 600 kvar at 525V then what it's rating at 415v.

2 Answers  


how we can convert 3 phase to single phase without using any transformer

8 Answers  


What is the use of Surge Capacitor in LAVT?

1 Answers   Snipe Engineers,


why we still use sinusoidal waveforms for transmission and utilisation (we know generation is sinusoidal), instead of other ac waveforms such as triangle, sawtooth, square etc.,? is there any mathematical derivations to prove sinusoidal is efficient than others?

1 Answers  


What is different between Metering CTs and Protection CTs?

4 Answers  


which connection is there in a rotor of the motor

2 Answers   All Trades Electrical, HAL,


I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.

1 Answers  


we often use the word HT (high tension) line.or we say HT switch gear, whats does HT basically mean. is it different from high voltage.

1 Answers  


give me the details of anti pumping relay

2 Answers  


RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED FOR OVER VOLTAGE PROTECTION SO WHY NOT THE RATING OF LIGHTENING ARRESTER BE MORE THAN 11KV ???????????????//

5 Answers   Hakel,


what is the difference between electrical and electronic choke?

0 Answers   TCS,


can we use 400w coke instead of 250w choke in 250w fittings

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)