how tan-delta test is performed?
Answer / k.prakashchandra
HV Tr ratio arm bridge is used for measurement of tan delta
and capacitance.The tests are conducted with 1.HV winding vs
LV winding grounded to tank.2.LV vs HV grounded 3. HV vs LV
ungrounded.4.Bushing insulation with respect to test tap.
The highest is selected .Test voltage is 2.5 to 15 KV for HV
and 1 to 1.5 KV for LV, in case of 110/11 KV Tr
| Is This Answer Correct ? | 3 Yes | 4 No |
How much inductance or resistance require as a starter in series with induction motor of specific capacity(e.g. 5 hp) ? What is formula for it ?
What is GIS Substation and how it operate? where these type of substation installed?
generator(Deutz 550kv)is runing for 2 hours with load of 900 amp and then it goes in shutdown with alarm fault messege of speed fault although heirtz reading fixed at 50,what does that mean
in single phase converter, the no.of scr's conducting during overlap a)1 b)2 c)3 d)4
how to calculate the ct burden?
What is the diff btw Conventional & Addressable Fire Alarm System???
what is creepage distance in sub-station?
What happens when reactive power enters a system?
in pf lagging means current decrease by increasing voltage is correct or not ? reason ?
what is the function of open delta System?
Why should we use Star-Delta connection in step down power transformers?
if u have to run a 300kw moter then what is ur choice HT or LT switchgear & explain why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)