can we use ACB for HT supply
Answers were Sorted based on User's Feedback
Answer / sheikh
I think ACB rated voltage is not more than 600V AC thereby
ACB cannot used in HT
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / jagsagar@rediffmail.com
ACB's are capable only upto 1000v. HT rating starts from 11KV,22KV.....132KV. Not possiblt to use ACB for HT.
Is This Answer Correct ? | 0 Yes | 0 No |
what precautions to be taken while desigining a LT,HT panel. Eg-LT panel PCC panel with ACB installed. HT panel VCB panel with VCB installed. & what is main diffrence betwn IP54 & IP55 construction of panel.
Why induction motor overheated?
2 Answers HVCC, Physical Research Laboratory (PRL),
What is the difference between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
How to calculate PF capactors for a connected load?
what is the working principle of electrical generator
What do you mean by ratio correction factor of instrument transformer?
What is sink and source?
How to Calculate 11 KV Side Cable size of a 250 KVA Oil cooled transformer
What happen if 200KVAR capacitor continuesly connected to load and all the plant machinaries are not in working?
show me the diagram of three phase wiring and also tell me hoe to take the readings of megger testing
How one can check the charger of the mobile phone or any other charger .......... that is it working ? if , working is it delivering the required supply which is needed by the battery to charge properly ?
State magnitude criterion.