what is surge impedance loading and it's significant in
power system?
Answers were Sorted based on User's Feedback
Answer / gautam kumar
SURGE IMPEDANCE LOADING (SIL)
The surge impedance loading or SIL of a transmission line is
the MW loading of a transmission line at which a natural
reactive power balance occurs. The following brief article
will explain the concept of SIL.
Transmission lines produce reactive power (Mvar) due to
their natural capacitance. The amount of Mvar produced is
dependent on the transmission line's capacitive reactance
(XC) and the voltage (kV) at which the line is energized.
In equation form the Mvar produced is:
Transmission lines also utilize reactive power to support
their magnetic fields. The magnetic field strength is
dependent on the magnitude of the current flow in the line
and the line's natural inductive reactance (XL). It follows
then that the amount of Mvar used by a transmission line is
a function of the current flow and inductive reactance. In
equation form the Mvar used by a transmission line is:
A transmission line's surge impedance loading or SIL is
simply the MW loading (at a unity power factor) at which the
line's Mvar usage is equal to the line's Mvar production.
In equation form we can state that the SIL occurs when:
If we take the square root of both sides of the above
equation and then substitute in the formulas for XL (=2pfL)
and XC (=1/2pfC) we arrive at:
The term in the above equation is by definition the "surge
impedance. The theoretical significance of the surge
impedance is that if a purely resistive load that is equal
to the surge impedance were connected to the end of a
transmission line with no resistance, a voltage surge
introduced to the sending end of the line would be absorbed
completely at the receiving end. The voltage at the
receiving end would have the same magnitude as the sending
end voltage and would have a phase angle that is lagging
with respect to the sending end by an amount equal to the
time required to travel across the line from sending to
receiving end.
The concept of a surge impedance is more readily applied to
telecommunication systems than to power systems. However,
we can extend the concept to the power transferred across a
transmission line. The surge impedance loading or SIL (in
MW) is equal to the voltage squared (in kV) divided by the
surge impedance (in ohms). In equation form:
Note in this formula that the SIL is dependent only on the
kV the line is energized at and the line's surge impedance.
The line length is not a factor in the SIL or surge
impedance calculations. Therefore the SIL is not a measure
of a transmission line's power transfer capability as it
does not take into account the line's length nor does it
consider the strength of the local power system.
The value of the SIL to a system operator is realizing that
when a line is loaded above its SIL it acts like a shunt
reactor - absorbing Mvar from the system - and when a line
is loaded below its SIL it acts like a shunt capacitor -
supplying Mvar to the system.
Figure 1 is a graphic illustration of the concept of SIL.
This particular line has a SIL of 450 MW. Therefore is the
line is loaded to 450 MW (with no Mvar) flow, the Mvar
produced by the line will exactly balance the Mvar used by
the line.
Is This Answer Correct ? | 39 Yes | 0 No |
Answer / swetha.t
A TRANSMISSION LINE'S SURGE IMPEDANCE LOADING IS SIMPLLY
THE MW LOADING ON IT WHEN THE LINE'S Mvar USAGE IS EQUAL TO
THE Mvar PRODUCTION
Is This Answer Correct ? | 5 Yes | 1 No |
can any one explain about when EB supply failed then how the load will transfer onto DG's step by step.
Why is it that North America uses 60 hz frequency while Europe uses 50 hz?
What are the advantages of individual drives?
1 Answers A1 Electricals, Suzlon,
How select ELCB for 32amp. socket having quantity 12Nos. We have to do this wiring in PLANT. Please Also explain the incoming cable specification.
0 Answers Gulf Industrial Services Company GISCO,
Why dont we get shock while testing for voltage with a line tester? How the bulb inside the tester glows while testing with tester coz we are totaly isolated from earth or we are not giving close path for the current to flow?
1 Ton is equal to how many watts?
L.A. (Lightening Arrester) is located at a place from where transmission line enters the transmitting substation. So L.A. (Lightening Arrester) is the first equipments which has to encounter with lightening, high voltage surges and switching surges. It has to absorb energy of lightening, high voltage surges, and switching surges. L.A. (Lightening Arrester) is made up of layers of semiconductors. If these layers can not tolerate energy released by lightening, high voltage surges, and switching surges the L.A. (Lightening Arrester) blasts.
If the Brush of DC motor is shifted by 90 deg, then what happens to voltage and torque? Both voltage and torque are zero. how to justify the answer?
How does CT can measure the high value DC current?
wat is the difference between BE &BTECH.
how to electrically make connection to ferroli GN2N?
sugest any typical project ?