Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF
COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SIZES??

Answers were Sorted based on User's Feedback



WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SI..

Answer / prakash suhane

Rating of cable depend on various factors like
1) Size of cable
2) No.of cores
3) Type of Insulation
4) Laying in air/ underground
5) Multi strand or single strand

Is This Answer Correct ?    144 Yes 7 No

WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SI..

Answer / vignesh

Current rating shall be decided by

* load requirement
* Power factor
* Voltage rating

Is This Answer Correct ?    71 Yes 7 No

WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SI..

Answer / piyush rana

There is no any thumb rule, therer is a standard table from
which we can know the capacity of the cable.
The current carrying capacity is depend upon the size of
conductor(Cross sectional area)

Is This Answer Correct ?    71 Yes 13 No

WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SI..

Answer / hdn electrical

There is no 'rule of thumb'. The current carrying capacity
of a cable can vary greatly depending on the location and
installation method in which it is used.

The tables in BS 7671 will show optimum carrying capacities,
but will then be subject to de-rating factors such as
ambient temperature, grouping, how it's fixed in/on a wall
or if it will be covered by insulation.

If you are unsure you should contact a qualified electrician.

Is This Answer Correct ?    22 Yes 4 No

WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SI..

Answer / gurupirit singh

The current carrying capacity
of a cable can vary greatly depending on the location and
installation method in which it is used.And also depend on
insulstaion & cooper of wire.

Is This Answer Correct ?    11 Yes 0 No

WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SI..

Answer / hariom

There is no 'rule of thumb'. Every manufacture provide their cables current carrying Data.It is almostly Same as per ISI.The current carrying capacity
of a cable can vary greatly depending on the location and
installation method in which it is used.

Is This Answer Correct ?    6 Yes 2 No

WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SI..

Answer / simon

The rule of thumb for current carrying capacity of copper
wire is 6 amperes per square millimeter of cross-sectional
area for an insulated, uncooled conductor.

Therefore the following applies:
1.0mm 6A
1.5mm 9A
2.5mm 15A
6.0mm 36A

Note that with air cooling, such as within an electric motor
or generator, the current carry capacity of the conductor
may be as high as five times the figures above (up to
30A/mm2) but is dependent on the efficiency of the cooling.

Is This Answer Correct ?    27 Yes 31 No

WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SI..

Answer / ramprakash

answer 9&12 is currect

Is This Answer Correct ?    0 Yes 8 No

WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SI..

Answer / sonu

current carrying capacity of wire's of
2.5 sq.mm=29amp
4.0 sq.mm=37amp
6.0 sq.mm=48amp
10.0 sq.mm=66amp

Is This Answer Correct ?    28 Yes 38 No

WHAT IS THE THUMB RULE FOR DECIDING THE CURRENT RATING OF COPPER WIRES SAY 2.5/4/6/10 MM SQUARE SI..

Answer / arun kr. singh

The Thumb rule is:

Size of cable x 4 = Current rating of cable.

e.g rating of 2.5mmsq cable is: 2.5x4=10A
for 4mmsq cable is: 4x4=16A
6mmsq cable is: 6x4=24A
10mmsq cable is:10x4=40A

Is This Answer Correct ?    7 Yes 23 No

Post New Answer

More Electrical Engineering Interview Questions

what is the total power generation in india?

0 Answers   GUVNL, HAL,


what parameters should we check to reduce the power bill

0 Answers  


Why is reating of t/f in kva but for inverter in kw ?

3 Answers   UPPCL,


Differentiate between magnetic field and magnetic flux?

0 Answers  


where any change in supply line due to the incipient faults in three phase induction motor

2 Answers   ABB,


which type of winding is used for high voltage & low current?

1 Answers   GEB,


What is diversity factor and how to calculate it

2 Answers   Al Faraa, Amul, Pentagon, Sobha Developers,


What is excitation?

2 Answers  


what transformer we used normally and upto which kva?

0 Answers  


what are the names and size of various conductors used in transmission lines

1 Answers   NTPC, Power Grid,


Can anyone provide with a SLD for HT panel installation for a 33KV line and distribution end has three 1.5MV transformers. Is it suitable to use OCB or VCB and also provide me the suitable rating and its connection diagram.

0 Answers   TATA,


What are types of losses in the Transmisson Lines ?

4 Answers   GE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)