how to amps calculate from 1KVA?
Answers were Sorted based on User's Feedback
Answer / pillay
1 KVA means 1000 volts amps for single phase calculations
1 KVA means 1000 volts amps x 1.732 for three phase
so for 240v single phase is 1000/240=4.16 A
SO FOR 3 PH @ 415 V= 1000/415/1.732=1.39A
SO FOR 3 PH @ 440 V= 1000/440/1.732= 1.31A
SO for easy average easy calculations you can take 1.35 AMPS
for 1 KVA for 3 p;h calculations
Is This Answer Correct ? | 30 Yes | 0 No |
Answer / kuldeep
KVA= Rt.3 VI from this formula we can find out Current.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / psk
1000/220=4.5 A for single phase
PF will come into picture only if it is in Kilowatt. This is KVA rating
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / janakiraman
kva is nothing but the voltage and current are directly
propotinal and there is no phase difference between them.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / be1
KVA=S , so you should know that S=Rt.(R^2+Q^2)
S=P*pf ---- (pf means power factor)
S=U*I*pf but in 3 phases you have
S=Rt.3*U*I*pf
Is This Answer Correct ? | 1 Yes | 3 No |
Can anybody tell abt concrete encased earthing or grounding?
How we calculate airgap between phases & terminal box of the transformer? any formulae.
how to make an earthing certificate
How to test transformer
why does chattering take place in ac contactors? can it be avoided & what care does the manufacturer take to eliminate this phenomenon????
how freewheeling diode improves the powerfactor
dear friends, how to calculate "Gage" in copper wire , aluminum wire etc. have any formula?
why we store only dc in batteries ?
how many electricity poles are there and what are the names and their sizes.
HOW COULD A SINGLE PHASE INDUCTION MOTOR ROTATE IN OPPOSITE DIRECTION???
How addressable fire systems work? Pl. send details with architect.(Loop), also send details regarding Gas system. Pl. help me.Thanks
What happen if in three phase 440 v , when you check voltage by testor it glows except one phase and in the same time when you check by multimeter it shows 440 v in any two phase.what will be the reason...