Answer / tripti kumari
first we find the resistance of the lamp that is given by formula p=V*V/R
R=230*230/200=264.5 ohm
now current flow through the lamp when connected to the supply 115 V that is
I=V/R
I=115/264.5=0.435
now power draw by the lamp given by
p=V*I=115*0.435=50.025
so it is slightly more than 50 W.
Is This Answer Correct ? | 94 Yes | 45 No |
Answer / roy
find amp draw (200W/230V); find resistance 230V/amp draw; find amps at 115V; I^2*R=Power consumed. 50.2Watts
Is This Answer Correct ? | 43 Yes | 18 No |
Answer / satheesh
The above answer is also wrong and Ist answer i
correct.Since the bulb is rated for 230 V and the power is
200W only at rated voltage.So the resistance is constant for
this rating.v2/w=230^2/200=264.5 ohms.If we apply 115 V also
this resistance will not vary.So the current drawn at this
time is v/R=I=115/264.5=0.435A=So definitely power = V*I
115*.435=50 Watts.
Is This Answer Correct ? | 21 Yes | 16 No |
Answer / pratik khodake
The correct answer is slightly more than 50W.
Is This Answer Correct ? | 15 Yes | 12 No |
Answer / sachin prajapati
(1) R=V1^2/P=230^2/200=264.5
V2=115
P=V2^2/R=115^2/264.5=50W
(2) R=264.5
I2=V2/R=115/264.5=0.435
P=V2I2=115×0.435=50.025W
So answer can both
Is This Answer Correct ? | 5 Yes | 5 No |
Answer / raghavendran.r
The above mentioned answer is wrong.Plz do remember that at any condition the power consumes by an equipment will not change from its designed value.
If you are operating a system at reduced voltage then to meet with the power requirement it will consume more current, rather than operate at less power.
So if the voltage is reduced by half, the current has to increase accordingly.
V*I = P;then 230*I = 200;I = .87A.
for V = 115 then current = 1.732A.
Is This Answer Correct ? | 4 Yes | 12 No |
1. If we apply dc supply to the primary winding of transformer it will be burnt out. similarly dc supply is given to field winding of syn. motor and armature winding of dc motor, they are safe. (Remember both windings inductive nature) what is the reason behind that?
Why Current Transformers cannot be connected in parallel
why is fan rotating slow speed, what is the problem?
at meter room 50 hrc switch installed,but there are not get earthing proper,so what happen?and 11kv transformer out put going in to hrc main 400a three nog each? so earthing is require for all switch? (some customer made earthing at there home.)
0 Answers Ebrahim Textile, Siemens,
why ahould you show client/engineer activities clearly on the project plan
what is the criteria for selecting fuse rating in 1phase, 2phase & 3phase welding sets?
What is the resistance of human body from head to toe?
10 Answers Bhel, Getco, Infosys,
8. A DYNAMOMETER TYPE WATTMETER RESPONDS TO THE.......
what is the difference between thermal magnetic release and microprocessor based release breakers. what are the advantages of latter over the first one...
5 Answers Jackson, Karthik Industries, McD BERL, TCS,
I completed iti in2004 I was worked in A grade contractor can I get c licence
Which level of the Transformer oil got dielectric strengh? And why?
explain working principle of earth leakage relay
0 Answers Divis Laboratories, SMIORE,