What is difference between miniture circuit breaker and
module case circuit breaker up to 63Amp.
Answers were Sorted based on User's Feedback
MCB can be used for only over current triping.
MCCB can be used for over current and earth fault(in built)
triping.
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / petrit hajrizi
Can we use MCCB to protect the cable for termal and short
cicuit.
| Is This Answer Correct ? | 5 Yes | 1 No |
MCB- is genarally used for lighting, it is fixed Rating
like: 2A, 6A, 10A,16A,20A,32A,63A. it will trip at any time
current carrying more then its rating.BUT MCCB- is genaraaly
using for Power sources, it is working range of current.
like: 4 -6A, 6-10A, 10-16A. it will use for Varies settings
have to set.
| Is This Answer Correct ? | 5 Yes | 2 No |
And also difference in short circuit current carrying
capacity.MCB having max up to 25kA. MCCB having up to 50KA.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / pgr ram
MCbs can withstand fault current upto 9KA. whereas MCCBs
can withstand high fault current upto 100ka. Hence MCCBs
are recommended to install at high current distribution
systems. Whereas MCBS are used for feeder distribution.
MCCB cost very high when compared to MCB
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / abracadabra
the difference between mcb and mccb is the difference of
adjusting tripping characteristics. this adjustment is
possible in mccb. the higher current making and breaking
capacity is one of the difference but the main reason is
the tripping char adjustment.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / timbadiya dixit
MCB is use only for over Load protection and MCCB is use to
over load and under load protection And MCCB is one types
of circuit Brecker.
| Is This Answer Correct ? | 3 Yes | 7 No |
How can get elongation of 2 k.G aluminium, if elongated aluminium dia is 2.5 mm?
clarify types of motor operated valves and advantages
if we put a energy meter in 500 kvar capacitor bank ,then how much units show in energy meter per day.
please give me all the Alarm .Trip ,Safety Relays & Conditions of Diesel-generators mail me on ashokbabunhce@gmail.com
My load is 1635 KW. & current pf is 0.884, I have to improve it for 0.99.Please suggest what KVAR value is needed?
difference between crane drive and line drive.
can we use relay in fan?
what is difference between delta-delta,delta-star transformers ???
The magnitude of sum of two sinusoidal av voltage is equal to 230 volt.the magnitude of each individual voltage is also equal to 230 volt.what must be the phase difference between voltages?
0 Answers PGVCL Paschim Gujarat Vij Company Limited,
what is protections used for 6.6kv ht motor
1.wat is the advantage of induction motor? 2.wat is diffrence between 1-phase and 3-phase induction motor?
How many speed of dg start motor for engine starting time
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)