Sir
Power transformer :- (in generating station)
Alternator terminals side - Delta
HT transmission line side - Star
Why?
Answers were Sorted based on User's Feedback
Answer / anup mohan
I could not understand the question clearly... but.. in generating n transmitting the terminals are in delta... as we need only 3 phases..... but at the other end.. i.e on the distribution end.. the connections are in star/wye... thtas ca.. in addition to the 3 phases we need a neutral... we ve neutral conection only in star and not in delta
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / nagarajan
Example 15mva,220/132kv
Star 220kv here phase voltage =line volatge/1.732=127kv
delta 11kv here phase voltage =line volatge.
Because star side we have neutral ,a.insulation cost less and 127kv insulation is sufficient but in this delta we require 132kv insulation.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kc
To reduce the fault level
The fault on primary side ie Y (LLG)
Will reflect as a LL Fault
So fault current level will b less
No zero sequence current ll b appar on d secondary side
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bhim kumar yadav(l&t)
bcz in delta side voltage is more compare to star side. so
insulation cost is very-very high in delta side compared to
star side.therefor, we keep always star connection in HT
side
| Is This Answer Correct ? | 2 Yes | 3 No |
can we measure +,-.zero sequence current ....? if so how can ???
What is the requirement of sulphuric acid in electrical feild?
c++ write a program to use a fuction call "max"which accepts an intger arrey of size5.as an arrument and return the larger and smallest of the arrey to main without changing. the original changing of the original position of the element of the arrey.
why there using acb enclosure in big buildings
what will be the minimum megger value for 132 Kv (earthed) potential transformer
When VFD is connected to a 3 phase main supply there is load current difference between incomer to VFD and outgoing from VFD.
why do we measure VIBRATION in -24vdc and why we adjust gap voltage -9vdc to 10-vdc? i am trying to get this information since 5 years, yet i haven't get reliable answer, i hope i can get from you.
Why NGR is provided in sub station?
How to discuss the phase shift of transformer considering open delta?
Why DG set rating in KVA
how calculate gd2 of ht motors
0 Answers Hindustan Copper Limited,
Why the Potential transformer Primary in connected to Earth?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)