Sir
Power transformer :- (in generating station)
Alternator terminals side - Delta
HT transmission line side - Star
Why?
Answers were Sorted based on User's Feedback
Answer / anup mohan
I could not understand the question clearly... but.. in generating n transmitting the terminals are in delta... as we need only 3 phases..... but at the other end.. i.e on the distribution end.. the connections are in star/wye... thtas ca.. in addition to the 3 phases we need a neutral... we ve neutral conection only in star and not in delta
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / nagarajan
Example 15mva,220/132kv
Star 220kv here phase voltage =line volatge/1.732=127kv
delta 11kv here phase voltage =line volatge.
Because star side we have neutral ,a.insulation cost less and 127kv insulation is sufficient but in this delta we require 132kv insulation.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kc
To reduce the fault level
The fault on primary side ie Y (LLG)
Will reflect as a LL Fault
So fault current level will b less
No zero sequence current ll b appar on d secondary side
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bhim kumar yadav(l&t)
bcz in delta side voltage is more compare to star side. so
insulation cost is very-very high in delta side compared to
star side.therefor, we keep always star connection in HT
side
| Is This Answer Correct ? | 2 Yes | 3 No |
why master trip(86) used in eletromagnet?
what is deffrent alternatid and gernater
what is the grounding Calculation formula? spouse i want to provide grounding to 3phase 18kw motor or i want to provide ground to 3phase 10kva dry type transformere or you give me any exemple...... Thanks.
what are 3 factors when selecting a contactor for a job?
WHAT IS FORMULA TO KNOW TO BACKUP TIME OF POWER PLANT 48V/50AMP DELTA POWER PLANT
which pump used in WTP explain the function of VFD how to dtermine capacitorbank of capacity one plant
why burdens of VTs is more than CTs?
What is the deffrence between Siemens S7-300 & S7-400 PLC?
When do you use a VFD motor?
two 100W/230V bulb are connected in series. what would be the voltage drop across 1 bulb
why are caluculte transformers or dg's in kva does not caluculate in kw
how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)