Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to calibrate a capillary type level transmitter for a
closed tank in field?
also what is the procedure for commissioning a capillary
level transmitter for a closed tank?

Answers were Sorted based on User's Feedback



how to calibrate a capillary type level transmitter for a closed tank in field? also what is the p..

Answer / aftab ahmed mazari

There are two methods: 1. workshop calibration, 2. field
Calibration.
Suppose you installed transmitter at vessel and want to
calibrate it.Follow following field procedure:
1. Close process side valves of both upper and lower
flanges.
2. Lose upper remote seal from process flange, It should
not get any pressure from process.
3. Remove lower side transmittrer flange from process side
flange. (It will be high side of transmitter)
4. Put your local made calibration flange at transmitter
remote seal and apply pressure.
(This flange must be same level of vessel flange from where
you removed it)
Suppose transmitter range is 0 to 1000 mm of H2O.
5. Apply this supply to your connected flange and take
readings at 0, 250, 500, 750, 1000 mm of H2O.
aftabmazari@yahoo.com

Is This Answer Correct ?    12 Yes 7 No

how to calibrate a capillary type level transmitter for a closed tank in field? also what is the p..

Answer / imran mansuri

capillary type tranmitter using remote seals and capillary
tubes filled with liquid of known of known density so if
you wanna callibrate it just close block valve just before
capilary @ high side & connect druck apply it's calibrated
range pressure as normal calibration ensure low side block
valve must be closed & if you asking commissioning so this
is not a DP type pressure tx so simple if you wanna put in
servie this tx just open high side block valve & than low
side block

Is This Answer Correct ?    10 Yes 13 No

Post New Answer

More Instrumentation Interview Questions

how magentic flow tx. vortex flow tx & ultrasonic flow tx works and its prinicle?its callibtration prosedure?

1 Answers  


How to force the bit in GE Mark V?

1 Answers  


How hart protocol can be connected with control valves?

0 Answers  


What is the processor scan time of allen bradle control logix processor 5555 lenin lenin123us@rediff.com

1 Answers  


Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.

0 Answers  


if field commnictor 475 does not communicate with transmitter what will you do ?

4 Answers   Samsung,


Valve positioner and actuators in detail.

0 Answers   MIEPL,


how to calibrate corollaries (Mass flow meter)?

0 Answers   Honeywell,


what the pid setting in controller

2 Answers  


how will do square root transmitter calibration

2 Answers   Roche,


Which types of quections asked in interview for FORMULATION PLANT (PHARMA)

0 Answers  


What pressure transmitter.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)