There are two methods: 1. workshop calibration, 2. field
Calibration.
Suppose you installed transmitter at vessel and want to
calibrate it.Follow following field procedure:
1. Close process side valves of both upper and lower
flanges.
2. Lose upper remote seal from process flange, It should
not get any pressure from process.
3. Remove lower side transmittrer flange from process side
flange. (It will be high side of transmitter)
4. Put your local made calibration flange at transmitter
remote seal and apply pressure.
(This flange must be same level of vessel flange from where
you removed it)
Suppose transmitter range is 0 to 1000 mm of H2O.
5. Apply this supply to your connected flange and take
readings at 0, 250, 500, 750, 1000 mm of H2O.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 12 Yes | 7 No |
Answer / imran mansuri
capillary type tranmitter using remote seals and capillary
tubes filled with liquid of known of known density so if
you wanna callibrate it just close block valve just before
capilary @ high side & connect druck apply it's calibrated
range pressure as normal calibration ensure low side block
valve must be closed & if you asking commissioning so this
is not a DP type pressure tx so simple if you wanna put in
servie this tx just open high side block valve & than low
side block
| Is This Answer Correct ? | 10 Yes | 13 No |
What is PDS and PDMS ?
why do 4 mA serves as 0% not 0 mA?
why we use -ve voltages in vibration prob?
pls tell me whethere flame proof HMI's are available or every HMI is manufactured by considering flame proof standard.
what is installation and commissioning of (fat & sat) of power plant dcs ? this question keeps in desirable conditions of one company .
Q- In the process of checking AC through Phase Tester our body is the part of circuit but we don't recevie Shock, Why ?
What is a PID?
what is the difference between 2 wire and 3 wire RTD- application wise,cost effectivity?
kindly tell where orifice,nozzle,air foil,ventury used in flow measurement?
Basic working principle of control valves
Difference between ultrasonic flow meter and radar type flow meter
2 Answers Dodsal, Qatar Petroleums,
if a dp transmitter has range 100 in H2O and flow is 20mmcf and if the flow is changed to 25 mmcf then what is the formula to determine new range of transmitter
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)