Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


if only one generator is running in droop mode parrallel
with grid and suddenly grid breaker off what will happen?
It will trip o/u freq or stay as it is? (urgent)

Answers were Sorted based on User's Feedback



if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off w..

Answer / suresh

It will iland mode but load to be as per generation extra
load to be disconnected immidiatly

Is This Answer Correct ?    6 Yes 0 No

if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off w..

Answer / kintoko adji

It's all depend on load and generator capacity, if load is
greater than generator capacity. If the load is much
greather than generator capacity (exam : 2 times of gen
capacity, it may trip because of under frequency, but
usually overload will be trip the generator CB first), but
if gen capacity is bigger than load, it will stay as it is.

Is This Answer Correct ?    3 Yes 0 No

if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off w..

Answer / hamid

If this happen then turbine rpm and exactly frequency goes
up and depending on reaction of your control system to speed
variation , speed may be control or just lock out relay of
generator operate and turbine should not trip .

Is This Answer Correct ?    1 Yes 0 No

if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off w..

Answer / mr.engineer

If you Have Island mode and you configuer it to switch from
deoop mode to Island mode at Grid tripping time, Your
system dose not effected by O/U freq.
Otherwise your system will trip due to underfrequency.

Is This Answer Correct ?    2 Yes 1 No

if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off w..

Answer / ramesh

Hello Guys

The question has been asked without giving details what
this generator was doing. That is whether it was supplying
inhoue load with additional power drawn from grid or the
genrator was meeting inhouse load and exporting power.

The reply would depend on this.

Is This Answer Correct ?    2 Yes 1 No

if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off w..

Answer / ismail yasin

genrator not alone together 4 steam turbine and all the
machine we are keeping droop mode all the time(with
parallel grid &islande mode.And we have separate load and
freq control systems. My question is when the machine
working alone and droop mode how will get freq reference?
and when parallel gird how will follow grid freq?

Is This Answer Correct ?    0 Yes 0 No

if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off w..

Answer / mukhtar fouad

This is depend on what`s the mode of the grid? switching
off the mode of grid by operator to disconnect the grid
system mode,then the one genrator will continue running
without load and stay as it is (droop mode)

Is This Answer Correct ?    0 Yes 1 No

if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off w..

Answer / darshan thakur

When grid breaker trip at that time turbine comes in island mode
frequency goes to higher side,but if governor response as per
load through . When Grid trip governor will transfer from drop
mode to isochronous mode.

Is This Answer Correct ?    0 Yes 1 No

if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off w..

Answer / atul pradhan

Paralelling with grid mean your DG is running on stand by
mode or droop mode, your systems load is on grid. when grid
trips all load shifted on DG WITHOUT INTERRUPTION when grid
power comes check synchro. relay gives command again to DG
& it will again run on droop mode.

Is This Answer Correct ?    1 Yes 6 No

if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off w..

Answer / vinod.t

when grid breaker trips..your generator is overloaded
suddenly frequency falls(47.75hz to 47hz depends on load)
and get trip on under frequency

Is This Answer Correct ?    3 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

I have recently seen a transformer which had two primary terminals and was connected between two lines,i would like to know what kind of transformer is it?short discription about it,any advantages,purpose of usage of the same.............

8 Answers  


Can any one give an explanation about rating factors of cable? if we are laying the cable on the air with an temp 15 degree then rating factors will be 1.15 and if we are laying the cable on the air an temp 60 degree then rating factor will be 0.76 please describe it and what is the difference between rating factor and derating factor?

0 Answers  


is the secondary voltage of current transformer greater than primary voltage,,,,,,,,] give the example with ct burden,current ratio,and primary and secondary side voltage?

2 Answers  


resistance of transformer oil=?

1 Answers   HCL,


what are the types of cables?

3 Answers  


What is difference between dc three point starter and dc four point starter?

3 Answers   Chettinad,


what happens when back feeding supply accidently collapses with normal supply ??? How?? [that is sometimes in a substation 11kv feeder if their ws long time permit work, back feeding supply will provide from nearest substation... if accidently after the permit work,they charged the feeder without removing back feeding wat will happen...?]

1 Answers   KSEB,


WHY EXCITER PHASE SEQUENCE ARE OPPOSITE THAN STATOR SUPPLY PHASE SEQUENCE IN SYNCHRONOUS MOTOR >

0 Answers  


what is the meaning of the parameters labeled on the surge arrestor like 150/20 ???

3 Answers  


What is the meter used to check the DG sound level.and pollution check

2 Answers  


how can we rotate a single phase motor (without cap.)in reverse direction?

2 Answers  


What is the disadvantage in proportional controller?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)