if only one generator is running in droop mode parrallel
with grid and suddenly grid breaker off what will happen?
It will trip o/u freq or stay as it is? (urgent)
Answer Posted / darshan thakur
When grid breaker trip at that time turbine comes in island mode
frequency goes to higher side,but if governor response as per
load through . When Grid trip governor will transfer from drop
mode to isochronous mode.
| Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
WHAT IS THE WINDING PROCEDURE OF ELECTRICAL MOTOR
how does a shunt reactor maintains the bus voltage???
when we have to purchase the transformer by own i.e how much load will preferred HT connection?
What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.
In all analog voltmeters or ammeter showing some small size symbols. as well as a star and in star 2no. digit, resister symbol,and other. what is that's meaning ?
What is class ab operation?
why they were using TRIAC instead relay in some controllers and what is the advantages.
explanation of mesh bus bars
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault
Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz
On what basis do you decide the ONAN (Oil Natural air natural) or Dry type transformer for a project?
What is an iron loss or core loss pi?
What is the Current equation in series RLC circuits.
what is the star delta connetion and how can do it a three phase motor with control witing with picture
What is the general power factor & min. power rating of TV,LCD type TV, CRt type TV, Scanner, printer?