if only one generator is running in droop mode parrallel
with grid and suddenly grid breaker off what will happen?
It will trip o/u freq or stay as it is? (urgent)
Answer Posted / darshan thakur
When grid breaker trip at that time turbine comes in island mode
frequency goes to higher side,but if governor response as per
load through . When Grid trip governor will transfer from drop
mode to isochronous mode.
Is This Answer Correct ? | 0 Yes | 1 No |
Post New Answer View All Answers
How many types of electrical earthing are there?
how to select the no. of brushes in a lap winding?
ow can i get certificate of competency as electrical supervisor and my diploma in electrical engineering from jalgaon.
Why the cores of large transformers build up of circular cross section?
Dear sir, In our plant have Station Transformer having capacity,i want to know, why LV side 40 - 40MVA is given? & how we can get 6.3 KV supply from tertiary(i.e. Open delta connection), Vector Group YNyn0 - yn0 +d MVA Rating 80MVA / 40 - 40MVA + 26.7MVA Voltage rating 420 (Tap range +6,to -10)81.25% /11.5KV - 11.5KV +6.3KV
Why derating factor os applied on Cables?
what is the difference between Central Battery System and UPS in applications and uses? and why UPS suitable for Computers and central battery for emergency lighting?
Good day everyone,currently in our premise we using 30kw slip ring motor with resistance bank which we use as forward and reverse at conveyor bar handling. So,my question is how do we calculate the resistance bank which is suit the motor. Kindly,assist me... thank you
Electronic circuit
electrical
What is the lifetime of a Thyristor? Is there a recommended lifetime for thyristors after which they should be replaced?
Describe Non I.S. Earth System and why is it used?
dear sir/madam i want to get some knowledge about RRB EXAMINATION(section engineer) 1- what is minimum cut off 2- wht portion is major portion . 3- can any body provide Sample paper. thanks & regards ashish
oil cooled transformer
What Should be the value of Vector Surge angle at Tripping and how to calculate it?