Resistor switching is used in which type Circuit Breaker
?
a) oil filled CB b) Air blast CB c) Gas filled CB
Answers were Sorted based on User's Feedback
Answer / j.kesavan
oil circuite breaker only resistanceswitching.
Is This Answer Correct ? | 36 Yes | 25 No |
Answer / sangram
Air Blast CB. High restriking voltage appears across the
contacts because of current chopping. If these voltages are
not allowed to discharge, they may cause break down of
insulation of the circuit breaker or the neighboring
equipment.
Is This Answer Correct ? | 11 Yes | 2 No |
Answer / raul
ABCB.......during current chopping, capacitive current breaking.......high transient voltages r produced......resistance switching avoids dis by connecting a shunt resistance across d cb contacts.......
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / nikhil sharma
oil filled circuit breakers use resistor switching to
balance the voltage distribution amongst the contacts of
circuit breaker and to reduce the transient overvoltages
produced during arc inhibition process...
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / srinivas.k.p
b)Air blast c.b in that we reduce the re-striking voltage b\w the moving contact and fixed contact by using the resistance and allows the current though reverse leakage current will be avoided only we resistance used in air blast c.b other than we can't use in oil r gas..
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anup $ingh
Obviously Air Blast Circuit Breaker
See.. http://www.oocities.org/hemant_thermal/airblastcircuitbreaker.htm
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / alpesh
can anybody tell me what is the use of that resistor switch???
Is This Answer Correct ? | 2 Yes | 3 No |
Why transformer called by KVA?
rajha power sector details
n1 =1000 n2 =?;v1 =200:v2 =400
Why compensation is necessary in feedback control system?
40 HP motor how many square mm size wire use for stator to motor & aluminium wire use ?
How can we define 'Phase'
What is Phasing out test?
What is the purpose of taking Capacitance and Tan Delta Test in Transformer bushing?
for a 500 KVA connected load, I calculated 30% of capactor for power correction. Even after using 225 KVR capactor PF is not improving. What could be reason for low Phase correction factor?
What is system earthing?what are the types?
What is the effect of pi controller on the system performance?
what is surge??