Answer / asif.k64@hotmail.com
KW=KVA*P.F
4.7=KVA*0.8
KVA= 6KVA approx
However the starting current is 16A hence we require a DG
of higher capacity.
This can be achieved by using a 7KVA DG.
| Is This Answer Correct ? | 5 Yes | 1 No |
xpression 'document.FrmQF.myemail' [
I WANT HOW CALCULATE TO CABLE FOR WELDING PLANT ?
how much the voltage & resistance should be ,between earth & neutral points.?& why?
What is phase cross over frequency?
Leakage current,un balance current which relay using for high voltage transmission?
Classify drilling machines.
What are the basic properties of signal flow graph?
hi this toufik here. i am doing my b.e.degree.now i am in final year and supposed to do a project in this year so i thinking to control the buchholz relay using software base means checking the status of transformer oil using microcontroler, plc or scada. so can i do so...??? alz suggest me...
what is the effect of back reactive power on the generator ?
what type of relay has to be used for tripping the circuit from mains when a fault occur in a machine
What is the GNA & MNA in armature reaction of Dc Generator
what is the role of energy meter in distribution system ???? technical and non technical losses in distribution system????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)