What is the difference between AMF panel and DG
Synchronization panel? please define the working of both
the panels?
Answers were Sorted based on User's Feedback
AMF Panel: is Auto Mains failure panel. When the EB power
goes off with a time delay signal will go to DG self
starter to start the DG. And when the EB power
resumes,after definite time delay stop signal goes to DG
and EB supply contactor will become ON.For a fraction of
time power will not be there for the utilities.
In synchronization, there is no outage of supply to the
utilities.When the incoming genset is to synchrinize with
the existing set,we've to match the magnitude of the
voltage, phase angle and the frequency and then only we've
to switch on the incoming set's breaker.
| Is This Answer Correct ? | 85 Yes | 10 No |
Answer / bhupinder singh verma
AMF Panel: is Auto Mains failure panel. When the EB power goes off with a time delay signal will go to DG self
starter to start the DG. And when the EB power
resumes,after definite time delay stop signal goes to DG
and EB supply contactor will become ON.For a fraction of
time power will not be there for the utilities.
In synchronization OF DG SETS, When the EB power goes off with a time delay signal will go to DG self starter to start the DG AND WHEN THE LOAD REACH THE 90% CAPACITY OF THE DG-1 THEN THE DG-2 WILL START AND THE DG-2 gen-set is to synchronize with the existing DG-1 THEN ,we've to match the magnitude of the voltage, phase angle and the frequency and then only we've to switch on the incoming set's breaker. THATS WHY THE OUT PUT SUPPLY SUPPLY OF BOTH DG SET WILL RUN ON THE SAME COMMON BUS BARS ( MEANS- DG-5OO KVA / DG-2 380 KVA THEN THE TOTAL LOAD IS 780 KVA ON COMMON BUS BARS ) IN THIS WAY WE CAN SYN. ELECTRICAL CITY BOARD POWER AND DG POWER ALSO.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / ajith kumar.s
1 st answer is right
but synchronization of palel is deffernt types one is rpm
synchronizing other is voltage and phase sequency this
uesed dark lamp or synchrocape used,
| Is This Answer Correct ? | 11 Yes | 13 No |
whycircuit breaker is not connected at the generator end where the capacity of the generator is more say 60MW, 100MW etc.
ult of expression 'document.FrmQF.myem
Upload data by LSMW via BAPI in SAP system.
Meaning of CTPT ,how it works &how it measures the reading on trivecter meter,&what is trivecter meter
1 Answers PF, Student, TSSPDCL,
How big (size) can the tertiary winding be in transformer? Can we load the tertiary winding, if yes then how much we can load it?
which type of starter is suitable for single phase motor ?
Why use only DC supply to charge batteries why not AC Supply??
all details of DG UPS HVAC
draw a dol with the following rtds,stop/start,ct,vt and o/l supply is 6.6kv and the coil is 110v
How do we find the rating of a transformer, if it got burnt badly.
Define current?
How to select HT/MV cable size ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)