what is the CT of protection and CT of metering ? what is
class 5P10 & 5P20 and class PS ?
Answers were Sorted based on User's Feedback
Answer / siva
Two type of core in ct,
1,protection core
2,metering core
protection core; only for protect the equipment used to
relay based.
metering core : this is only for showing the current in
ammeter .
In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-accuracy class.
p- protection
10-10% error.
20-20% error.
protection class:it is calculated by the knee point voltage
test.
| Is This Answer Correct ? | 6 Yes | 18 No |
Answer / kiran
CT for protection means for protecting other equipment in
the ckt. based on the protection class ex:5P10
5 - % of accuracy
P - for protection
10- 10% of rated current also it withstood
CT ratio 300/1A 10% of rated value means it can withstand
upto 3000A if any abnormal condition.
Normally for metering we use CL:1 , 0.5 ,0.2 because for
metering accurate value we need.
econamy purpose we won't use 1P10 or 0.5P10 and also
protection we don't want that much accuracy.
Class PS : based on knee point voltage we caliculate PS.
this is for special purpose.
| Is This Answer Correct ? | 13 Yes | 26 No |
Answer / saravanan
Two type of core in ct,
1,protection core
2,metering core
protection core; only for protect the equipment used to
relay based.
metering core : this is only for showing the current in
ammeter .
In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-accuracy class.
p- protection
10-10% error.
20-20% error.
protection class:it is calculated by the knee point voltage
test.
| Is This Answer Correct ? | 15 Yes | 59 No |
Answer / arunmozhi
there are two type of ct in field,
1,protection CT
2,metering CT
protection CT; only for protect the equipment used to
relay based.
metering CT : this is only for showing the current in
ammeter .
In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-acurancy class.
p- protection
10-10% error.
20-20% error.
ps class:it is calculate to the knee point voltage.
| Is This Answer Correct ? | 20 Yes | 74 No |
Answer / anil konkimalla
Protection CT doesnt need much accuracy and it should not
saturate in fault condition. PS class means protection
class CT. 5P10 means 5% is the maximum composite error
shown while 20 times fault current flows.Hence 5P10 is
superior comparing to 5P20
| Is This Answer Correct ? | 63 Yes | 122 No |
Answer / syed naveed akhter
ct can use as protuction in supply lines where 3 phase use
in different areas saperatly for example in lighting in
hall, if current pass throw one phase high then ct detect
emf out side the wite and generate some supply to cut the
main source.
as you know that ct is current transformer, it fix around
the wire where current flow. when load take some current
then out side of wite some emf produce which detect by ct
and its pass some voltage which use to measure (it is a
calculation which i dont know) help to metering.
| Is This Answer Correct ? | 8 Yes | 68 No |
why do we carry out winding resistance test?
0 Answers MahaGenco, MAHINDRA,
In case of motor Power Factor Generally We Apply A Capacitor But How Can We Know That A Motor is Running On Very low Power Factor And What Rating Of Capacitor We Have To Place And Tell Me Conversion Of Micro Farad to KVAR>
Why all transmission lines are AC, not DC line?
working principle of AC Servo Motor with its construction
WHY THE TRANSFORMER VALUE MEASURES IN KVA INSTEAD OF KW.
1.what is surge used in power system 2.what is switching used in power system 3.what is lightning used in power system
gd eve frndz my qstn is how convert sound energy to electrical energy
What is the difference between hot and cold loop testing?
Why the standard of ambient teperature mentioned as 40 degree celcius in machines.
give single line diagram of D.O.L and star -Delta starter ?
8 Answers ABS, Al-Shuaah, Alkali Metals, Cabin Crew, Cognizant, CRI, Gwalior Distilleries, Hotels, Logicon Engineers, Max India, Nicomet, Radisson Blu, RK Company, Siemens, SLCM, Solar, Steel Strips Wheels, Sugar Factory, TATA, TCS,
primary of transformer connected to Dc supply in series with switch, and secondary connected on ammeter, what happens when swith On and OFF. (or) if continuously On and OFF
Whether IP65 enclosure box blocks ventilation if driver for LED have to enclosed inside IP65 box
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)