what is the CT of protection and CT of metering ? what is
class 5P10 & 5P20 and class PS ?

Answer Posted / arunmozhi

there are two type of ct in field,
1,protection CT
2,metering CT
protection CT; only for protect the equipment used to
relay based.

metering CT : this is only for showing the current in
ammeter .

In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-acurancy class.
p- protection
10-10% error.
20-20% error.

ps class:it is calculate to the knee point voltage.

Is This Answer Correct ?    20 Yes 74 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

WHY IS THE EARTH FAULT CURRENT ALWAYS LESS THAN THE NORMAL CURRENT??

1756


What is the difference between electronic regulator and ordinary rheostat regulator for fans?

576


What happens if the series current double?

1006


How can we calculate the efficiency of a Running (On-Load) Motor ? What parameters are required and what is the method ?

1534


WHAT IS THE DIFFERENCE BETWEEN GENERAL INVERTER AND SOLOR INVERTER TELL ME PLZ

1670






How npn and pnp transistor works

646


What is the formula to calculate the no load current of a single & three phase induction motor

1773


bus bar design conditions and sizing pls tell me quickly

1491


Application Comparison between 22KV (UE)and 33KV (E) system. Are we allowed to use 33KV (E) cable in lieu of 22KV (UE) cable. What are the technical disadvantages.

2298


1 Ton is equal to how many watts?

675


why burdens of VTs is more than CTs?

1352


what is the calculation involved to design the heater to heat 10KL of water in temperature control unit?

1484


What is meant by time harmonics and space harmonics?

2372


what will be the min and max voltage flow from neutral to earth?

951


how balanced in star delta connection ?

1636