1.Difference between vcb and Acb and partes.
2.Difference between STS and ATS.
Answers were Sorted based on User's Feedback
Answer / thowsif_emerson
1.VCB= vacuum circuit breaker normally used in HV
applications.
ACB = Air circuit breaker, normally used in LV
applications.
2.There are two main technologies used for these devices
with different characteristics in terms of
switching quality and cost each having its merits and
deficiencies: Static Transfer Switches
(STS) and Automatic Transfer Switches (ATS).
A>STS is based on static electronic components (SCR)
therefore allowing for a fast and precise
control of the switching between one line and the other.
This solution permits to obtain a perfect
Break Before Make (BBM) behaviour by never permitting a
source overlap. Moreover, it is also
capable of very fast switching between the two sources with
a max delay of less than 5 msec
(typically 4 msec).
B>ATS is based on electromechanical components where the
BBM switching is actually made by
controlling the relays on each source line. This kind of
technology can still make a perfect Break
Before Make change of supply sources both in synchronous
and asynchronous conditions but it
is certainly slower than the static solution.
| Is This Answer Correct ? | 10 Yes | 0 No |
Is there any question in the name of Static Switch in UPS??
Wht ar the reason for low voltage on consumer side?
basic princple of induction and synchronous motor
How to perform a DC resistance test In Alternator and their proceduces?
what is advantage of providing taping on HT side?
WHAT IS DIFFERENCE BETWEEN PHASE CONVERTER AND VFD
What is the possible cause for failure of lightning arrestors in outdoor substation under normal condition
What is the operating range of voltage and current in grid supply in India?
how can we find of cable capicity in amper?how much ampere withstand by 300sqmm cable?
what will happen if frequency is below 50 hz?
if you asked to choose a ckt breaker from MCB & MCCB for 32A which one will be best and why??
length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)