Why is the diffrential protection in DG. What if the CT
polarity is reversed while connecting for the same type of
protection? How polarity can be made ok?
Diffrential protection is used to protect internal fault
like winding faults,it is used to protect the the
equipments like Generator,Transformer and bus bars.
If CT polarity changed in Directional type releys it will
give trip command when normal operating condition.
Brfore giving connection we must read name plate details to
avoid polarity change.
| Is This Answer Correct ? | 17 Yes | 2 No |
what is tower earthing and what for it is required
How to find out freqency in Ac and Dc and also how u control it
What is the effect on in Zone and out zone fault if Phase side CT is Vk/2<30 mA and Neutral side is CT is Vk/4<30 mA for Transformer REF protection
How many safety of Disel Generator
How to calculate no of Lighning arrestors are required for protecting 50mX 50m*20m cubical building and locations of LA?
How does a television work?
Which device is used for the source of emission of electrons in a crt?
Can we use all 3 cores of a cable to connect DC motor + ve terminal and similarly one more cable for - ve terminal.
Hp to Kw and Kw to I(amps) conversion......
1) why a dg set shows variation of power factor and load when synchronised with other dgs? 2)Why the load sharing is not become equal in all dgs?. 3)When a dg set will not run on auto start?
what are carbondioxide and dcp used in fire extinguishers
different between electrical and electronics Engineering????
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)